New postby chris mc on Mon Dec 13, 2010 9:17 pm

Codeman,
In a 3 story SFR that has an elevator are the doors at each level required to be fire rated? These doors are to be provide by the builder and match the other interior doors, they are not part of the elevator system. We are under the 2006 IRC (til January 1st)
chris mc
 
Posts: 22
Joined: Mon Mar 22, 2010 10:36 pm

Re: Elevator

New postby Jerry Peck - Codeman on Tue Dec 14, 2010 8:32 pm

Hi Chris,

Not that I have found for single family dwellings.

The IRC has limited, specifically stated, requirements for shafts, which is what the elevator shaft falls under. The following are the limited and specifically stated requirements for shafts in the IRC:

- SHAFT. An enclosed space extending through one or more stories of a building, connecting vertical openings in successive floors, or floors and the roof.

- G2415.1 (404.1) Prohibited locations. Piping shall not be installed in or through a circulating air duct, clothes chute, chimney or gas vent, ventilating duct, dumbwaiter or elevator shaft. Piping installed downstream of the point of delivery shall not extend through any townhouse unit other than the unit served by such piping.

- E3302.2 Penetrations of fire-resistance-rated assemblies. Electrical installations in hollow spaces, vertical shafts and ventilation or air-handling ducts shall be made so that the possible spread of fire or products of combustion will not be substantially increased. Electrical penetrations through fire-resistance-rated walls, partitions, floors or ceilings shall be protected by approved methods to maintain the fire-resistance rating of the element penetrated. Penetrations of fire-resistance-rated walls shall be limited as specified in Section
R317.3.

Note the reference to R317.3, which is "Dwelling Unit Separation", which is not applicable here.

Think of the elevator as a stairway with intermediate landings which have doors at those intermediate landings - there is no requirement for fire-rated doors there either.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Elevator

New postby chris mc on Tue Dec 14, 2010 9:45 pm

Jerry Peck - Codeman wrote:
Think of the elevator as a stairway with intermediate landings which have doors at those intermediate landings - there is no requirement for fire-rated doors there either.


Great example! Thank you very much.