Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

THIS BOARD IS READ ONLY AS CODEMAN HAS RETIRED
NO NEW QUESTIONS WILL BE PROCESSED

|
AskCodeMan.com
|

Custom Search

Fire resistance on under side of stairs.. residential

Fire resistance on under side of stairs.. residential

New postby bigdog on Wed Mar 02, 2022 2:15 pm

2 story home built in 2008 Boynton Beach. The wooden stairway to the 2nd floor is boxed / drywalled in under the stairs. There is a small door that accesses this area and is being used for storage currently. The wooden stairway inside this area is exposed. I believe this now requires the under side of the stair structure to be drywalled....am I right?

David
bigdog
 
Posts: 85
Joined: Thu Apr 12, 2012 10:54 pm

Re: Fire resistance on under side of stairs.. residential

New postby Jerry Peck - Codeman on Wed Mar 02, 2022 10:40 pm

David,

From the 2004 Florida Building Code, Residential
- R311.2.2 Under stair protection. Enclosed accessible space under stairs shall have walls, under stair surface and any soffits protected on the enclosed side with 1/2-inch (12.7 mm) gypsum board.

From the 2007 Florida Building Code, Residential
- R311.2.2 Under stair protection. Enclosed accessible space under stairs shall have walls, under stair surface and any soffits protected on the enclosed side with 1/2-inch (13 mm) gypsum board.

From the 2010 Florida Building Code, Residential, that section was moved to here:
- R302.7 Under-stair protection.
- - Enclosed accessible space under stairs shall have walls, under-stair surface and any soffits protected on the enclosed side with 1/2-inch (12.7 mm) gypsum board.

From the 2014 Florida Building Code, Residential )in the 2014 edition:
- R302.7 Under-stair protection.
- - Enclosed accessible space under stairs shall have walls, under-stair surface and any soffits protected on the enclosed side with 1/2-inch (12.7 mm) gypsum board.

Now, let's go back to the 2001 Florida Building Code:
- The 2001 Florida Building Code (the Building and Residential code were one and the same) exempted out stairways in dwelling units from under stair protection.
- - 1006.1.1 Enclosed stairways
- - - (blah, blah, blah)
- - - - Exceptions:
- - - - - 1. Stairways serving and contained within a dwelling, dwelling unit, or hotel suite.
- - 1006.1.4 There shall be no enclosed, useable space within an exit enclosure, including stairs.
- - - (blah, blah, blah)
- - - - Exceptions:
- - - - - 2. Protection is not required for those stairways exempted from enclosure in 1006.1.
- - 1007.1.3 Interior stairs constructed of wood, except those with open risers, shall be fireblocked as specified in 705.3.
- - - (blah, blah, blah)
- - - - Exception: Protection is not required for those stairways exempted from enclosure in 1006.1.1.
- - 1007.1.4 The underside of interior stairways, if of combustible construction, shall be protected to provide not less than 1-hour fire resistance.
- - - (blah, blah, blah)
- - - - Exception: When located within a dwelling unit.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Fire resistance on under side of stairs.. residential

New postby bigdog on Sun Mar 06, 2022 9:03 pm

Thanks for the info Jerry!
bigdog
 
Posts: 85
Joined: Thu Apr 12, 2012 10:54 pm


Return to Fire-rated assemblies: Fire walls, fire partitions, smoke barriers, ceiling-floor, ceiling-attic; Separation of garages from dwelling unit; Separation between structure's exterior walls and property line



Who is online

Users browsing this forum: No registered users and 2 guests


cron