Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|

Custom Search

Attic & fireblock

Attic & fireblock

New postby Marc M on Fri Mar 02, 2012 3:53 am

Hey Jerry, is there a fireblocking conflict by having a door that leads into an attic in a hallway that also acts as an attic over the existing structure?
SECTION R807
ATTIC ACCESS
R807.1 Attic access. Buildings with combustible ceiling or
roof construction shall have an attic access opening to attic
areas that exceed 30 square feet (2.8 m2) and have a vertical
height of 30 inches (762 mm) or greater. The vertical height
shall be measured from the top of the ceiling framing members
to the underside of the roof framing members.
The rough-framed opening shall not be less than 22 inches
by 30 inches (559 mm by 762 mm) and shall be located in a
hallway or other readily accessible location. When located in a
wall, the opening shall be a minimum of 22 inches wide by 30
inches high. When the access is located in a ceiling, minimum
unobstructed headroom in the attic space shall be 30 inches
(762 mm) at some point above the access measured vertically
from the bottom of ceiling framing members. See the California
Mechanical Code for access requirements where mechanical
equipment is located in attics.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: Attic & fireblock

New postby Jerry Peck - Codeman on Fri Mar 02, 2012 1:50 pm

No conflict with the two as fireblocking is for blocking off concealed spaces, such as wall stud spaces, from the attic.

An example of fireblocking for walls is at the floor, at the ceiling, and 10 feet horizontally.

The intent is to block the spread of fire from vertical spaces (such as walls) from horizontal spaces (such as floor and ceiling areas) and vice versa.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: Attic & fireblock

New postby Marc M on Fri Mar 02, 2012 11:47 pm

Sure thing, vertical.. thanks so much.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am


Return to Fire-rated assemblies: Fire walls, fire partitions, smoke barriers, ceiling-floor, ceiling-attic; Separation of garages from dwelling unit; Separation between structure's exterior walls and property line



Who is online

Users browsing this forum: No registered users and 1 guest