We are designing a new project located in Mamaroneck, NY. It is a 4 story mixed use building. It is a R-2 IIIB Construction. The interior is sprinkled. We need to put windows in a wall that is located 3'2" from the side property line. The total wall opening % for the windows is around 22%. The approach we are taking to get to less than 15% protected openings is to make most of the windows 45 minute fire-rated assemblies and for the remaining windows to be 1 hour rated assemblies so that these can qualify as a wall and not count as an opening. Is this the right approach in regards to the fire-ratings? We are trying to use steel frame windows made by Optimum.
Thanks.
Mike NY
 
Posts: 3
Joined: Thu Mar 13, 2014 2:18 pm

Re: Fire-rated window assemblies close to side property line.

New postby Jerry Peck - Codeman on Mon Mar 17, 2014 7:51 pm

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Fire-rated window assemblies close to side property line.

New postby Mike NY on Tue Mar 18, 2014 11:50 am

Thanks for your answer. The sprinkler system is NFPA 13, Not NFPA 13R, according to the sprinkler plans.
There is one thing that I am not clear about. If a window assembly is one-hour fire rated for both sides, does it technically count as a wall and not an opening?
Mike NY
 
Posts: 3
Joined: Thu Mar 13, 2014 2:18 pm

Re: Fire-rated window assemblies close to side property line.

New postby Jerry Peck - Codeman on Tue Mar 18, 2014 10:16 pm

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm