DWV within shared wall townhouse

DWV within shared wall townhouse

New postby Marc M on Thu Apr 03, 2014 1:47 am

Hey Jerry, I have a question regarding DWV within a common wall separating a townhouse / two adjoining units. If there are plastic dwv within this wall, how can it be effectively sealed when its plastic and two, per the exception below in bold; what is the "or what". Meaning, what is the fix if there is dwv within this wall? Hopefully I explained this well enough..

R302.2 Townhouses. Each townhouse shall be considered a
separate building and shall be separated by fire-resistancerated
wall assemblies meeting the requirements of Section
R302.1 for exterior walls.
Exception: A common 1-hour fire-resistance-rated wall
assembly tested in accordance with ASTM E 119 or UL
263 is permitted for townhouses if such walls do not contain
plumbing or mechanical equipment, ducts or vents in
the cavity of the common wall.
The wall shall be rated for
fire exposure from both sides and shall extend to and be
tight against exterior walls and the underside of the roof
sheathing. etc...
You do not have the required permissions to view the files attached to this post.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: DWV within shared wall townhouse

New postby Jerry Peck - Codeman on Thu Apr 03, 2014 7:52 am

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: DWV within shared wall townhouse

New postby Marc M on Thu Apr 03, 2014 10:41 am

I was hoping you weren't going to confirm what I suspected. It this image consistent with what you are describing?
You do not have the required permissions to view the files attached to this post.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: DWV within shared wall townhouse

New postby Jerry Peck - Codeman on Thu Apr 03, 2014 11:38 am

Basically, yes.

There could also be one common wall constructed as a 2 hr rated wall, with proper firestopping (versus fireblocking) for each item in that wall.

Of course, trying to construct a single common wall which will remain standing when the structure on one side falls is a bit difficult (unless the common wall is either CMU or poured concrete).
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: DWV within shared wall townhouse

New postby Marc M on Fri Apr 04, 2014 10:31 am

All clear now, thanks much Jerry.