Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

THIS BOARD IS READ ONLY AS CODEMAN HAS RETIRED
NO NEW QUESTIONS WILL BE PROCESSED

|
AskCodeMan.com
|

Custom Search

Fire separation of garage

Fire separation of garage

New postby bigdog on Tue May 20, 2014 10:37 am

Hi Jerry
Are you allowed to have open wood framing ceiling and walls in an attached wood frame garage and house? This was an addition in PBC. Its open to the house attic which I know is wrong but is that and a rated fire wall between them the only real requirements?
I have found out the addition (1989) failed an inspection and the owner builder never fixed the problem and left the permit open

David
bigdog
 
Posts: 85
Joined: Thu Apr 12, 2012 10:54 pm

Re: Fire separation of garage

New postby Jerry Peck - Codeman on Tue May 20, 2014 4:13 pm

David,

The garage/living space separation requirement is minimum 1/2" gypsum board on the garage side of the wall separating the two.

The 1/2" gypsum board may be on the garage side of the wall and extend to the underside of the roof decking above, or the 1/2" gypsum board may be on the garage side of the wall and on the ceiling of the garage. Either option separates the garage from the living space and the attic above the living space.

The garage side of that wall is not allowed to be up stud walls - first would be the requirement for insulation in the stud bays to serve as the thermal envelope for the living space, second would be the separation requirement for minimum 1/2" gypsum board on the garage side of that wall.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm


Return to Fire-rated assemblies: Fire walls, fire partitions, smoke barriers, ceiling-floor, ceiling-attic; Separation of garages from dwelling unit; Separation between structure's exterior walls and property line



Who is online

Users browsing this forum: No registered users and 1 guest