Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|

Custom Search

Fire-stopping Draft-stopping CMU/Frame Construction

Fire-stopping Draft-stopping CMU/Frame Construction

New postby Tampatundra on Fri Jun 16, 2017 7:00 pm

Please take a quick look at the two pictures I've attached.

Subject: 2 story new home construction (Florida) with CMU first level, Framing second level

Do you see anything wrong with either picture?

The horizontal 1x4 furring strip on the 1st floor (CMU wall) is attached on top of the RMAX foam insulating board. Is this acceptable for fire blocking or draft stopping.
The horizontal 2x4 furring strip on the 2nd floor (Frame Construction) is attached directly to the studs and the RMAX is under the furring with additional furring running vertical.

I am unable to find the code reference that specifically details the requirement, if any, for fire-stopping or draft-stopping for this particular scenario.

Any assistance will be greatly appreciated.

Fire1sm.JPG

Fire2sm.JPG
You do not have the required permissions to view the files attached to this post.
Tampatundra
 
Posts: 3
Joined: Mon Jun 05, 2017 12:37 pm

Re: Fire-stopping Draft-stopping CMU/Frame Construction

New postby Jerry Peck - Codeman on Sun Jun 25, 2017 10:33 pm

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Fire-stopping Draft-stopping CMU/Frame Construction

New postby Tampatundra on Mon Jun 26, 2017 5:19 pm

1. Is the downstairs block construction considered combustible construction?
2. Can the drywall serve as the fire blocking? Normal 1/2" Gypsum Drywall

What I'm inferring from your response is that RMAX foam board insulation is not a listed fire blocking material, and therefore the horizontal furring should be attached directly to the block/CMU wall to provide the necessary fire blocking required. (side note: RMAX does make a fire rated foam board insulation, but for this application, is not that type)

As for the floor truss: good eye there! I did not catch that. The installer properly attached the shim to the engineered truss.

Your response would be appreciated. Thank you
Tampatundra
 
Posts: 3
Joined: Mon Jun 05, 2017 12:37 pm

Re: Fire-stopping Draft-stopping CMU/Frame Construction

New postby Jerry Peck - Codeman on Mon Jun 26, 2017 8:03 pm

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Fire-stopping Draft-stopping CMU/Frame Construction

New postby Tampatundra on Wed Jun 28, 2017 6:22 pm

Jerry,

Thank you again, for your quick and thorough response. It is much appreciated.

In conclusion, regarding the horizontal furring on CMU construction:

Picture 1 shows the RMAX installed against the CMU wall, and the horizontal 1x4 furring installed on top of the RMAX. Is this a code compliant installation? Or, does the horizontal furring need to be installed onto the CMU wall, and the RMAX up to the bottom of the 1x4 furring?

"the draftstopping referred to in the code statement is the concealed space" But, the concealed space is filled with the RMAX foam board insulation (in the example whereby the RMAX is installed on top of the RMAX.

Thank you.
Tampatundra
 
Posts: 3
Joined: Mon Jun 05, 2017 12:37 pm

Re: Fire-stopping Draft-stopping CMU/Frame Construction

New postby Jerry Peck - Codeman on Wed Jun 28, 2017 7:11 pm

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm


Return to Fire-rated assemblies: Fire walls, fire partitions, smoke barriers, ceiling-floor, ceiling-attic; Separation of garages from dwelling unit; Separation between structure's exterior walls and property line



Who is online

Users browsing this forum: No registered users and 7 guests