by Jerry Peck - Codeman on Fri Jun 12, 2009 9:20 pm
Hi Jake,
The 2006 IRC states that section slightly differently, and that difference makes all the difference when reading it.
From the 2006 IRC. (underlining and bold are mine)
- R312.2 Guard opening limitations. Required guards on open sides of stairways, raised floor areas, balconies and porches shall have intermediate rails or ornamental closures which do not allow passage of a sphere 4 inches (102 mm) or more in diameter.
- - Exceptions:
- - - 1. The triangular openings formed by the riser, tread and bottom rail of a guard at the open side of a stairway are permitted to be of such a size that a sphere 6 inches (152 mm) cannot pass through.
- - - 2. Openings for required guards on the sides of stair treads shall not allow a sphere 4 3/8 inches (107 mm) to pass through.
The maximum allowable size for a sphere is 4 inches, except ...
- except at that triangular area = 6 inches
- except at the side of the stair treads = 4-3/8 inches
If you code states it differently, would you please post the exact wording and the code it is from? Thank you.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired