by Jerry Peck - Codeman on Fri Jul 24, 2009 11:49 pm
Hi Harris,
The only code section which would apply specifically would be the energy code for air infiltration and exfiltration and the weather resistance of the wall cladding (the brick, masonry, wood, stucco, etc.).
The energy code is easy to address on masonry, stucco, wood, HardiePlank and similar claddings (siding) as you should be able to seal the penetration to resist air infiltration and exfiltration with a good quality sealant.
On brick veneer, though, the air barrier is actually back inside the wall behind the brick where you cannot access it. The brick is approximately 4 inches thick, there is at least a 1 inch air space between the brick and the wall - at least that is required to be there, making the water-resistive barrier (WRB) back at least 5 inches from the face of the brick. About your only hope of sealing that would be if the rubber sleeve you are using is at least 6 inches long, coat the inboard end with sealant, slide the rubber sleeve into place, and before the outer flange its home against the brick is to seal the back of the flange where it meets the brick and push the rubber sleeve home to meet the face of the brick.
Keep in mind that there will not be any way of knowing how well sealed the actually air barrier (vapor retarder, really) is to the rubber sleeve, but there is only one other choice (unfortunately it is a common choice) and that is to do it like the phone company, cable company, and satellite dish companies do it ... drill the holes and ignore any real attempt at sealing things back up. NOT GOOD but is unfortunately all too common for the "care less", it's-not-my-house-so-I-don't-care, installers.
Now, with regards to leaking and weather protection of the exterior cladding, masonry, wood, HardiePlank, and similar claddings (sidings) will be the same as for the energy code and sealing to protect against air infiltration and exfiltration.
The same problem will occur with brick veneer for weather protection too.
Stucco on frame (masonry and stucco on masonry are the same, this is stucco on frame) creates a different headed monster as the house has the same or similar WRB as for brick veneer, except that where brick veneer has a minimum 1 inch air space where water penetrating through the brick and mortar will drain down the back face of the brick (when the brick is laid up properly), the stucco will have the WRB as that drainage plane, right up against the sheathing which is behind the WRB.
To complicate matter even more, the stucco has a paper backed metal lath fastened over the WRB with the stucco applied directly to that paper backed metal lath. There is minimal space between the paper backing of the lath and the WRB. The paper backing on the lath serves as a bond breaker to keep the stucco from adhering to the WRB and to create that every-so-slight drainage plane.
Here is the problem with stucco on frame: When you drill that hole through the wall you are drilling that hole through the drainage plane and have no way to seal at the drainage plane without sealing everything else up. You have just create a potential leak through the stucco on frame wall system. Again, and unfortunately, phone, cable, and satellite dish installers drill those holes and have no regard for what they are doing, slap some sealant on it and then they walk away to their next installation to repeat the same problem all over again.
The problem comes about because water DOES GO THROUGH STUCCO, and it does drain down that drainage plane of the WRB, and you are now dealing with trying to keep that water (granted, not a lot of water, but it is there) from entering through the hole you drilled and getting behind the WRB where you do not want that water.
There is no easy answer for drilling holes through stucco on frame. The real solution is to properly flash in a sleeve during construction of the stucco on frame wall system as that is really the only way to keep the water out.
Masonry, stucco on masonry, wood, HardiePlank, and similar claddings should be easy to deal with.
Vinyl siding and aluminum siding not only have similar problem with the actual drainage plane being back behind the surface you are working with but also need attention to allow for expansion and contraction movements, which you penetration and antenna lead would restrict.
Brick veneer, you can come close.
Stucco on frame, you just have to do your best at trying to seal it all up all the way back along the sleeve and cross your fingers the penetration does not create a problem water intrusion-wise.
Hopefully the information above is helpful in you trying to do the penetration the right way, or at least the best way possible.