aaronm wrote:How does this affect the size and configuration of interior doors in rooms without windows and in hallways?
Aaron,
From the 2009 IRC (is that still what Texas is using?):
- R311.1 Means of egress. All dwellings shall be provided with a means of egress as provided in this section. The means of egress shall provide a continuous and unobstructed path of vertical and horizontal egress travel from all portions of the dwelling to the exterior of the dwelling at the required egress door without requiring travel through a garage.
- -
(Jerry's Note: The means of egress is only required to be "continuous", "unobstructed", "from all portions", and "to the exterior", which means that, unless additional requirements are specified below, those are the only requirements.) - R311.2 Egress door. At least one egress door shall be provided for each dwelling unit. The egress door shall be side-hinged, and shall provide a minimum clear width of 32 inches (813 mm) when measured between the face of the door and the stop, with the door open 90 degrees (1.57 rad). The minimum clear height of the door opening shall not be less than 78 inches (1981 mm) in height measured from the top of the threshold to the bottom of the stop. Other doors shall not be required to comply with these minimum dimensions. Egress doors shall be readily openable from inside the dwelling without the use of a key or special knowledge or effort.
- -
(Jerry's Note: "Other doors shall not be required to comply with these minimum dimensions.", this can be taken two ways - a) as meaning that only the one ("at least one") required egress door to the exterior must meet those size requirements and other doors which egress to the exterior do not have to meet those requirements as they are not "the" "required egress door", the other doors are just 'doors to the exterior'; or b) as meaning that every ("at least one") side-hinged door which egresses to the exterior is "one of the" "required egress door"s and must meet those sizes. However, any door which is does not egress to the exterior, or egresses to the exterior but is not side-hinged, is not an "egress door" and does not have to meet those size requirements - this includes side-hinged doors which lead to a garage as the means of egress is not permitted to go through a garage.) - R311.6 Hallways. The minimum width of a hallway shall be not less than 3 feet (914 mm).
- -
(Jerry's Note: That one is clearly written - "minimum width", "hallway", and "not less than 3 feet".)So now we go the definitions, which (unfortunately) does not define "continuous" or "obstructed", however, the code tells us that the definitions in the other codes are to be applied for terms not defined in the IRC but defined in other ICC codes ... not that such is helpful as the other ICC codes do not define those terms either (not that I found). However, the code also states:
- R201.4 Terms not defined. Where terms are not defined through the methods authorized by this section, such terms shall have ordinarily accepted meanings such as the context implies.
- -
(Jerry's Note: We now use "ordinarily accepted meanings such as the context implies", which does not require anything special for "continuous" or "obstructed" ... as long as there is a "means of egress" provided.)Which takes us to this definition in the IBC:
- MEANS OF EGRESS. A continuous and unobstructed path of vertical and horizontal egress travel from any occupied portion of a building or structure to a public way. A means of egress consists of three separate and distinct parts: the exit access, the exit and the exit discharge.
- -
(Jerry's Note: Okay, that does not seem to help much ... except for this part "any occupied portion" ... which means we need to determine what an "occupied portion" means.)We have two definitions to choose from, one from the IRC and one from the IBC:
- From the IRC:
- - OCCUPIED SPACE. The total area of all buildings or structures on any lot or parcel of ground projected on a horizontal plane, excluding permitted projections as allowed by this code.
- - -
(Jerry's Note: From the definition of "occupied space", we can determine that "occupied space" is being related to the building area of the structure on a given lot; i.e., the "occupied space" of a 10 foot by 10 foot building on a slab on grade is 100 square feet, and the "occupied space" of a 10 foot by 10 foot building on piers with a crawlspace under it is also 100 square feet. This definition is not referencing the space inside which may be 'occupied' by the 'occupants' of the building.) - From the IBC:
- - OCCUPIABLE SPACE. A room or enclosed space designed for human occupancy in which individuals congregate for amusement, educational or similar purposes or in which occupants are engaged at labor, and which is equipped with means of egress and light and ventilation facilities meeting the requirements of this code.
- - -
(Jerry's Note: From the definition "occupiable space", we can determine that "occupiable space" is essentially the same as "habitable space" in the IRC, see below.) - From the IRC:
- - HABITABLE SPACE. A space in a building for living, sleeping, eating or cooking. Bathrooms, toilet rooms, closets, halls, storage or utility spaces and similar areas are not considered habitable spaces.
Summary of the above and R311.1:
- R311.1 Means of egress. All dwellings shall be provided with a means of egress as provided in this section. The means of egress shall provide a continuous and unobstructed path of vertical and horizontal egress travel from all portions of the dwelling to the exterior of the dwelling at the required egress door without requiring travel through a garage.
Thus, the requirement for means of egress "from all portions of the dwelling" essentially applies to the "habitable space" of the dwelling ... not to bathrooms, closets or every nook and cranny within the dwelling.