R302.5.2 Duct penetration

R302.5.2 Duct penetration

Postby Marc M on Sat Jul 30, 2011 12:04 am

R302.5.2 Duct penetration. Ducts in the garage and ducts
penetrating the walls or ceilings separating the dwelling
from the garage shall be constructed of a minimum No. 26
gage (0.48 mm) sheet steel or other approved material and
shall have no openings into the garage.

Jerry,
can you explain the last bolded sentence?
Also,
When the duct penetrates the firewall, is the entire duct on the garage side (for example) solid sheet metal? I asume it is for obvious reasons but want to make sure.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: R302.5.2 Duct penetration

Postby Jerry Peck - Codeman on Sat Jul 30, 2011 1:39 pm

Hi Marc,

Marc M wrote:and shall have no openings into the garage.

The duct is required to be connect to the air handler unit (the typical reason the duct would be in the garage) and run from the air handler unit through the garage space through the separation wall between the garage space and the living space, with; a) no supply openings; b) no cut out openings in the duct; c) no openings of any kind for any reason which open the duct to the garage space (also remember that the system serving the the living space is not allowed to have a supply or return in the garage, and this backs that up).

When the duct penetrates the firewall, is the entire duct on the garage side (for example) solid sheet metal?


Yes, 26 gage sheet metal all the way ... don't forget the "or other approved material" - that sometimes includes ductboard (depends on the AHJ, or in the cases of Florida the Residential code states, "shall be constructed of a minimum No. 26 gage (0.48 mm) sheet steel, 1 inch (25 mm) minimum rigid nonmetallic Class 0 or Class 1 duct board, or other approved material").
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: R302.5.2 Duct penetration

Postby Marc M on Sun Aug 07, 2011 6:12 pm

Thank you.