Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|
The following Codemen are available to answer your questions:
All Codes and Standards - Jerry Peck, Codeman


Q&A Board links
  • REGISTER

  • FAQ

  • LOGIN

  • Q&A BOARD INDEX

  • View New Questions

  • View Unanswered Questions

  • View Active Questions/Answers

  • Mark Questions as read

  • View Your Questions

  • Go To Your User Control Panel




  • Links to:
  • Construction Litigation Consultants


  • Florida Building Commission

  • Florida Building Codes Online


  • International Code Council

  • ICC Codes Free Online


  • Building Officials and Administrators of Florida




  • Product Approvals
  • Florida Product Approval

  • ICC Evaluation Reports Search

  • Miami-Dade NOA Search




  • Inspector and Contractor License Search
  • Search Florida Licenses




  • Technical links
  • Technical Information page


























































  • Contact Codeman



  • Custom Search

    What is actually consider a Bus or Busway

    What is actually consider a Bus or Busway

    New postby JohnSTI on Thu Aug 25, 2016 9:41 am

    In trying to interpret the understanding of using Flex Cord drops I continually run across the term 'Bus" or Busway". My understanding of these terms are to be related with "multiples" runs within a group such as in a tray (open or closed) not an individual run.
    for example;
    Branches from busways shall be permitted to be made in accordance with 368.56(A),(B),and(C).
    and
    368.56(B)(2) notes that for industrial installations with qualified personnel, it is permitted to install a flexible cable drop that is connected without an attachment plug, with no length limitation from the busway plug-in device to the tension take-up support, provided the cable is supported at intervals not exceeding 8 ft.

    What I'm trying to resolve is I have a circuit coming from a Main Panel box the is in metal conduit, running up and across the ceiling stops over a machine where it ends with a square electrical box or gang box if you will. Then a Flex cord drops down to the machine and the machine plugs into the drop end.

    My question is... "Is the span of conduit along with the electrical box considered a "Bus" or "Busway""? So that I know to apply any mentioned "Bus" or "Busway" requirements in the code to these components.


    Thanks guys
    JohnSTI
     
    Posts: 11
    Joined: Thu Nov 12, 2015 11:52 am

    Re: What is actually consider a Bus or Busway

    New postby Jerry Peck - Codeman on Thu Aug 25, 2016 3:54 pm

    JohnSTI wrote:In trying to interpret the understanding of using Flex Cord drops I continually run across the term 'Bus" or Busway". My understanding of these terms are to be related with "multiples" runs within a group such as in a tray (open or closed) not an individual run.


    First, let's define what a bus is and what a busway is:
    - a bus is typically a length of uninsulated or insulated, copper, aluminum, or brass metal bars, rods, or tubes.
    - a busway is:
    - - From the 2014 NEC - 368.2 Busway. A raceway consisting of a grounded metal enclosure containing factory-mounted bare or insulated conductors, which are usually copper or aluminum bars, rods, or tubes.

    What I'm trying to resolve is I have a circuit coming from a Main Panel box ...


    Let's clarify that "main panel" term - is that the "service equipment panel" or is that a downstream panel (not 'service equipment')?

    Many people use the terms "main panel" and "sub panel" yet do not always mean the same thing. A "service equipment" panel has the neutral bonded to ground, other panels have the neutral isolated from ground.

    Once we are past the 'where the neutral is bonded to ground' panel, all panels are the same.

    Getting back to your question of having a circuit coming out of a panel:
    in metal conduit, running up and across the ceiling stops over a machine where it ends with a square electrical box or gang box if you will. Then a Flex cord drops down to the machine and the machine plugs into the drop end.


    and

    My question is... "Is the span of conduit along with the electrical box considered a "Bus" or "Busway""? So that I know to apply any mentioned "Bus" or "Busway" requirements in the code to these components.


    No, that conduit is not a busway and does not contain bus sections. The requirements for bus and busways, and the permitted wiring methods for same, do not apply to the circuit in your description.
    Jerry Peck - CodeMan
    AskCodeMan.com

    Construction and Litigation Consultant
    Construction Litigation Consultants, LLC.
    ConstructionLitigationConsultants.com
    User avatar
    Jerry Peck - Codeman
    Site Admin
     
    Posts: 1103
    Joined: Fri Dec 12, 2008 12:06 pm


    Return to Definitions - Regardless of what other forum a defintion might fall under, place definition questions here



    Who is online

    Users browsing this forum: No registered users and 1 guest



    www.AskCodeMan.com
    cron