Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|

Custom Search

GFCI receptacles with a W

GFCI receptacles with a W

New postby Bill Kriegh on Fri May 15, 2009 8:29 am

From the UL White Book:
Weather-resistant Receptacles — Receptacles for use in wet and damp
locations in accordance with Article 406 of the NEC. Weather-resistant receptacles
are identified by the words ‘‘Weather Resistant’’ or the letters ‘‘WR’’
where they will be visible after installation with the cover plate secured as
intended.
Bill Kriegh
 
Posts: 3
Joined: Fri May 15, 2009 8:09 am

Re: GFCI receptacles with a W

New postby Jerry Peck - Codeman on Fri May 15, 2009 9:04 am

Hi Bill,

Your post relates to this question: viewtopic.php?f=3&t=107

Thank you for that information.

I was not connecting the 'W' with the 'WR', although it now seems so obvious.

Again, thank you.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: GFCI receptacles with a W

New postby Jerry Peck - Codeman on Mon May 18, 2009 11:55 am

Just adding more information from the UL White Book in case it is needed.

- Receptacle-type GFCIs for use in wet and damp locations in accordance with Articles 406 of the NEC are identified by the words ‘‘Weather Resistant’’ or the letters ‘‘WR’’ where they will be visible after installation with the cover plate secured as intended.
- Weather-resistant receptacle-type GFCIs installed in wet locations are intended to be installed with an enclosure that is weatherproof, whether or not the attachment plug cap is inserted.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm


Return to Electrical: Service Equipment, electrical panels, wiring, lighting, switches, receptacles, etc.



Who is online

Users browsing this forum: No registered users and 33 guests