Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|

Custom Search

150 amp residential panel on exterior wall in Garage!

150 amp residential panel on exterior wall in Garage!

New postby InspectorHolmes on Sat Aug 22, 2009 10:22 pm

I inspected a home where the panel is mounted on exterior wall line in a home built in the mid 70's.There is rusted spots which indicate moisture.I would not think this would be allowed by codes since exterior walls are insulated and water diffusion in the wall line.Could someone help me on this.I've looked in the NEC but to no avail.This doesn't seem right.
1) Safety from nails piercing conductors,water intrusion,and the close prox to combustible insulation required in exterior wall.

Please Help out if you can answer this one
InspectorHolmes
 
Posts: 4
Joined: Tue Jul 21, 2009 10:10 pm
Location: Atlanta,Ga

Re: 150 amp residential panel on exterior wall in Garage!

New postby Jerry Peck - Codeman on Sat Aug 22, 2009 11:35 pm

InspectorHolmes wrote:panel is mounted on exterior wall line


Would you clarify what you are describing?

Do you mean the enclosure is "surface mounted *ON* the wall" or "recess mounted *IN* the wall"?

1) Safety from nails piercing conductors,water intrusion,and the close prox to combustible insulation required in exterior wall.


Not sure what you are asking there, but here are my guesses as to what you are asking:
- NM cable requires protection plates when installed within 1-1/4 inch of the face of the stud.
- If an enclosure is in an area where it will get wet, such as outside, then it needs to be a raintight type enclosure.
- There are no requirements regarding electrical enclosure clearance to combustible material as the enclosure is not supposed to get that hot, and any fire caused by a problem in the enclosure is supposed to be contained in that enclosure.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: 150 amp residential panel on exterior wall in Garage!

New postby Joe Tedesco on Sun Aug 23, 2009 3:24 am

I will also add the following that seems to give a rule that can be considered here. It is short and sweet:

110.12(B) Integrity of Electrical Equipment and Connections. Internal parts of electrical equipment, including busbars, wiring terminals, insulators, and other surfaces, shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners, abrasives, or corrosive residues. There shall be no damaged parts that may adversely affect safe operation or mechanical strength of the equipment such as parts that are broken; bent; cut; or deteriorated by corrosion, chemical action, or overheating.

My thoughts lead me to the underrlined part here.
Joe Tedesco, NECĀ® Codeman
User avatar
Joe Tedesco
 
Posts: 25
Joined: Sat Aug 01, 2009 12:26 am
Location: Boston, Massachusetts

Re: 150 amp residential panel on exterior wall in Garage!

New postby CPetty on Sun Aug 23, 2009 11:03 pm

Thanks! The panel cover was rusting in many areas on the exterior.
There were no signs of water,however there were several double taps.
CPetty
 
Posts: 1
Joined: Sun Aug 23, 2009 10:46 pm

Re: 150 amp residential panel on exterior wall in Garage!

New postby Jerry Peck - Codeman on Mon Aug 24, 2009 12:21 pm

Is the enclosure recessed into the wall or surface mounted?

It makes a difference, other questions may follow which will also make a difference in how you write it up.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm


Return to Electrical: Service Equipment, electrical panels, wiring, lighting, switches, receptacles, etc.



Who is online

Users browsing this forum: No registered users and 1 guest