New postby garrett on Wed May 11, 2011 11:19 am

Is it permissable to install a 60 amp non fuseable disconnect on a 30 amp circuit for an a/c unit
garrett
 
Posts: 6
Joined: Thu Apr 28, 2011 1:34 pm

Re: a/c unit

New postby Jerry Peck - Codeman on Wed May 11, 2011 6:35 pm

Hi Garrett,

Yes ... as long as there is a properly sized overcurrent device at the supply of the circuit, and that practice is quite common too.

The overcurrent protection for the circuit conductors would be at the supply end of that circuit (at the panel the circuit originates from), all that disconnect would be doing is providing a means for the contractor to remove power to the a/c unit for servicing and not have to worry about someone restoring power to the circuit while they are working on the circuit or equipment.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired