AFCI BREAKER SEPARATION

AFCI BREAKER SEPARATION

New postby RICHARD TAN on Sat Jul 02, 2011 7:56 pm

Hi Jerry,

Electrical panel. Is it true that on the new NEC? AFCI breaker in the electrical panel required to be separated with other non AFCI bearker. I did a thermal scan on many AFCI breaker, I found many AFCI breaker temperature of 100F-104F. Is the AFCI breaker separation is to keep the breaker cooler? I have found only one electrical panel that was install this way on a newer home (2010), non in older home. Is this the new way to install AFCI breaker?

Thank's Richard
RICHARD TAN
 
Posts: 60
Joined: Wed Jan 14, 2009 9:43 am

Re: AFCI BREAKER SEPARATION

New postby Jerry Peck - Codeman on Sat Jul 02, 2011 10:15 pm

Hi Richard,

I will double check on that for you - if it is an 'NEC requirement' then I missed it.

Even though the various manufacturers have acknowledged the heat generated by AFCI breakers, and many verbally recommended separating the older AFCI breakers, they did not put that in writing.

Supposedly, the new AFCI breakers do not generate enough heat for that to be a problem. As such, there has been no requirement for separating AFCI breakers in a panel.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: AFCI BREAKER SEPARATION

New postby Jerry Peck - Codeman on Tue Jul 05, 2011 7:43 pm

Hi Richard,

As I thought, I could not find anything in the NEC regarding spacing AFCI breakers. This would be because each manufacturer would require that if their AFCI breakers produced too much heat to be installed side-by-side.

If one manufacturer did not require it and another manufacturer did, the manufacturer requiring that spacing would like be at a disadvantage in the marketplace.

You would need to read the installation instructions on the AFCI breaker to find out if there was any limitation regarding the installation of that particular manufacturer's AFCI breakers.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: AFCI BREAKER SEPARATION

New postby Marc M on Thu Jul 14, 2011 12:02 am

AFCI's and GFCI's are ALWAYS hotter than other disconnects when you scan via infrared.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: AFCI BREAKER SEPARATION

New postby Jerry Peck - Codeman on Thu Jul 14, 2011 12:38 pm

Marc M wrote:AFCI's and GFCI's are ALWAYS hotter than other disconnects when you scan via infrared.


Hi Marc,

GFCI breakers too?

Are you sure? I can't think of what would cause a GFCI breaker to be hotter.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: AFCI BREAKER SEPARATION

New postby Marc M on Thu Jul 14, 2011 2:59 pm

Yes you're correct. The afci disconnects and its GFI receptacles which show hotter. I mis spoke.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: AFCI BREAKER SEPARATION

New postby Jerry Peck - Codeman on Thu Jul 14, 2011 6:03 pm

Marc M wrote:its GFI receptacles which show hotter


Hi Marc,

I just cannot think of a reason why a GFCI protection device would show hotter than a similar non-GFCI protection device. The GFCI protection device does not use any voltage or current in the normal 'all is okay' mode - the GFCI protection device does not use any more current in the protection 'all is not okay' mode as it is getting ready to trip (which happens immediately when the threshold is reached). The GFCI protection device does, in the 'all is not okay' mode, actually create a very (and I do mean very) minute amount of current, but not enough to be measurable as far as heat goes, and the time from of that minute amount of current is quite brief too.

An AFCI protection device, on the other hand and as compared to a GFCI protection device, does use a small amount of power (current/voltage) to run its small inboard computer to monitor the circuit at all times. It is that small power used which does generate the heat which causes AFCI protective devices (i.e., AFCI breakers) to heat up. The AFCI breaker definitely heats up enough to see it with an infrared thermal imaging camera.

But a GFCI protective device heating up? That needs to be explained to me so I can figure out and understand what is going on which shouldn't be going on.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: AFCI BREAKER SEPARATION

New postby Marc M on Thu Jul 14, 2011 7:18 pm

Yea, I agree. I will scan one for you and send it. I see many IR reports where the tech will call out the GFI receptacle for this very reason. Anyhow, let em scan one and I'll shoot one over to you.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: AFCI BREAKER SEPARATION

New postby Marc M on Fri Jul 15, 2011 12:00 am

Here's a few from my house. I have 5 and all were fairly warm.
You do not have the required permissions to view the files attached to this post.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: AFCI BREAKER SEPARATION

New postby Marc M on Sun Jul 17, 2011 9:13 pm

Wudda ya think?
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: AFCI BREAKER SEPARATION

New postby Jerry Peck - Codeman on Mon Jul 18, 2011 12:39 am

Ummm ... somehow my response is gone ... maybe I went to edit it and deleted it?

I will have to type it again this evening.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: AFCI BREAKER SEPARATION

New postby Marc M on Mon Jul 18, 2011 12:45 am

No worries...take your time.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: AFCI BREAKER SEPARATION

New postby Jerry Peck - Codeman on Wed Jul 20, 2011 10:54 pm

Hi Marc,

Not sure what happened to my other post like this one, maybe I clicked 'Preview' instead of 'Submit', regardless, I am sure it was something I did and just did not catch it at the time - oh well.

What I had posted ... er ... thought I had posted ... was that I was asking if you would try to see what was actually hot and why.

For example, could you:
- remove that receptacle and take an image of each side and its back
- remove any conductors feeding off to downstream receptacles (to remove any load on the receptacle's terminals and to remove any current flow to/through the receptacle, then take images of the front, both sides, and the back
- with no other conductors other than the line connected to the receptacle, remove:
- - the ground and take images
- - the neutral and take images
- - the hot and take images

At some point that heat which is showing will go away, and depending on what is no longer connected and what is still connected will indicate what might be generating the heat. The simplest thing would be that it is heat from a load wired downstream from that receptacle and the current is heating up a terminal or something.

Will be interesting to have you tell me what you find out.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: AFCI BREAKER SEPARATION

New postby Marc M on Wed Jul 20, 2011 11:05 pm

I'll give it a shot this weekend, we'll see what happens.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am