Concrete-Encased Electrode
Posted:
Wed Aug 24, 2011 10:14 am
by aaronm
Does the NEC require that access be provided to the connection of the grounding electrode conductor to the concrete-encased electrode (UFER)? If so, where is this stated?
Thanks,
Aaron
Re: Concrete-Encased Electrode
Posted:
Wed Aug 24, 2011 10:19 am
by aaronm
I think I answered my own question in 250.68(A) x1
Re: Concrete-Encased Electrode
Posted:
Wed Aug 24, 2011 12:53 pm
by Jerry Peck - Codeman
The answer is both 'yes' and 'no'.
If the connection is encased in concrete, then, 'no' applies.
If they make the connection in the wall and it is not encased in concrete, then, 'yes' applies.