UFER CODE SECTION 1999 NEC

UFER CODE SECTION 1999 NEC

New postby gd_swin on Mon Nov 28, 2011 1:37 pm

Morning Jerry, hope you had a good holiday. Per our previous communication I need to know the code section from the 1999 NEC on UFER requirements. Thank you Gary
gd_swin
 
Posts: 1
Joined: Tue Nov 22, 2011 4:00 pm

Re: UFER CODE SECTION 1999 NEC

New postby Jerry Peck - Codeman on Mon Nov 28, 2011 6:55 pm

From the 1999 NEC: (bold and underlining are mine)
- 250-50. Grounding Electrode System
- - If available on the premises at each building or structure served, each item (a) through (d), and any made electrodes in accordance with Sections 250-52(c) and (d), shall be bonded together to form the grounding electrode system. The bonding jumper(s) shall be installed in accordance with Sections 250-64(a), (b), and (e), shall be sized in accordance with Section 250-66, and shall be connected in the manner specified in Section 250-70.
- - An unspliced grounding electrode conductor shall be permitted to be run to any convenient grounding electrode available in the grounding electrode system or to one or more grounding electrode(s) individually. It shall be sized for the largest grounding electrode conductor required among all the electrodes connected to it.
- - The grounding electrode conductor shall be unspliced or spliced by means of irreversible compression-type connectors listed for the purpose or by the exothermic welding process.
- - Interior metal water piping located more than 5 ft (1.52 m) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.
- - - Exception: In industrial and commercial buildings where conditions of maintenance and supervision ensure that only qualified persons will service the installation and the entire length of the interior metal water pipe that is being used for the conductor is exposed.
- - - - FPN: See Sections 547-8 and 547-9 for special grounding and bonding requirements for agricultural buildings.
- - (c) Concrete-Encased Electrode. An electrode encased by at least 2 in. (50.8 mm) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 20 ft (6.1 m) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than ½-in. (12.7-mm) diameter, or consisting of at least 20 ft (6.1 m) of bare copper conductor not smaller than No. 4. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means.

I.e., "If available on the premises at each building or structure served, each item (a) through (d), and any made electrodes in accordance with Sections 250-52(c) and (d), shall be bonded together to form the grounding electrode system"
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm


Return to Electrical: Service Equipment, electrical panels, wiring, lighting, switches, receptacles, etc.



Who is online

Users browsing this forum: No registered users and 1 guest


cron