by Jerry Peck - Codeman on Thu Dec 05, 2013 1:31 am
Bruce,
If this is elastic enough, but it might break if stretched that far:
- ARTICLE 406 Receptacles, Cord Connectors, and Attachment Plugs (Caps)
- - 406.4 Receptacle Mounting.
- - - (E) Receptacles in Countertops and Similar Work Surfaces in Dwelling Units. Receptacles shall not be installed in a face-up position in countertops or similar work surfaces.
"Looking for a reference to back up my statement this is dumb and oh by the way, wrong."
It is only dumb if the receptacle does not have a bubble cover (and, no, the code does not require a bubble cover in the cabinet under the sink, but common sense does).
Stretching the code that far ... I dunno.
I have one installed as you describe under our kitchen sink, however, not only do I have a bubble cover on it (in case there is a leak from above) but it is in a weather proof exterior type box and is a GFCI type to provide an additional layer of people protection.
Sometimes there is basically no other place to install the receptacle, when that is the case then extra steps for protection should be taken - not required to by the minimum code, but should be done based on common sense.
Jerry Peck - CodeMan