New postby Marc M on Mon Jan 27, 2014 10:59 pm

Hey Jerry,
you posted the comment below a while back. I was wondering if you have the actual book it came from, 1965-68? I was interested in see the actual code as it was written. if not no big deal, just thought id ask.



680-7. Grounding
- (a) All metallic conduit, piping systems, pool reinforcing steel, light fixtures, and the like, shall be bonded together and grounded to a common ground. The metal parts of ladders, diving boards, and their support, shall be grounded.
- (b) No pool equipment shall be grounded to an external grounding electrode that is not common to the pool ground (deck box or transformer enclosure).
- (c) An unbroken No. 14 AWG, or larger, insulated copper wire shall be provided for a grounding conductor from the deck box to the distribution panel ground.
- (d) Metallic raceways shall not be depended upon for grounding. Where exposed to pool water and in other corrosive areas such as in pump houses or adjacent to water treating and other equipment, the grounding of the non-current carrying parts shall be by means of an insulated copper conductor sized in accordance with Section 250-95.

The 1965 NEC was similar, expanded with some changes, and the grounding/bonding conductor went to a No. 8 AWG. There were other changes as well.

In the 1968 NEC the grounding/bonding changed to bonding and that is when the 5 feet horizontally of the pool water first came in.

You could say that pool bonding first came into the NEC in 1962, and that bonding as we know it today came into the NEC in 1968, albeit in a much simpler form. Equipotential bonding has continued to improve and change throughout the various code cycles since.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: Pool bond

New postby Jerry Peck - Codeman on Tue Jan 28, 2014 8:47 am

Marc,

I'll look back in those books for it and let you know.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: Pool bond

New postby Marc M on Tue Jan 28, 2014 12:26 pm

You bet.. Thanks J
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: Pool bond

New postby Jerry Peck - Codeman on Tue Jan 28, 2014 9:58 pm

That wording was from the 1962 NEC.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm


Return to Electrical: Service Equipment, electrical panels, wiring, lighting, switches, receptacles, etc.



Who is online

Users browsing this forum: No registered users and 1 guest