anti corrosive paste

anti corrosive paste

New postby bigdog on Thu Oct 22, 2020 11:22 am

Hey Jerry

Is anti corrosive paste required on aluminum feeder conductors in a interior distribution panel. 2018 commercial building 250 MCM

David McCabe
bigdog
 
Posts: 85
Joined: Thu Apr 12, 2012 10:54 pm

Re: anti corrosive paste

New postby Jerry Peck - Codeman on Thu Oct 22, 2020 11:41 am

David,

The NEC does not require anti-oxidant paste for termination of aluminum conductors into terminals.

Some manufactures put anti-oxidant in the terminals, other manufactures do not, however, most manufactures "recommend" using anti-oxidant paste when terminating aluminum conductors.

"Recommend", but not "require".

When finding work where the contractor did not follow "recommendations" by the manufacturer, that work may deserve a little closer look as other short cuts may have also been taken.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired