Hearthman wrote:Actually, the answer is right under our noses. IFGC 503.5.4 Chimney terminations ....."and is at least 2 feet (610 mm) higher than any portion of a building within a horizontal distance of 10 feet (3048 mm)."
We tend to think of this rule pertaining just to adjacent gable walls and such but it includes roof turbines because they are a "portion of a building". By locating 2 feet above this feature of the building, you get the flue gas outlet into clear, undisturbed wind and above this opening.
Though turbines normally exhaust, all it takes is a wind eddy to recirculate air. By maintaining this separation, you should reasonably prevent recirculation of flue gases.
Now, if you want, you could cite an ASHRAE Standard, 62.1, Ch. 5 that deals with such separations from 'hazardous exhausts' at a min. 15ft for normally bad stuff and 30 ft. separation for extra bad stuff. Based upon personal experience, I find the 2/10 rule sufficient.
Marc M wrote:From the 2006 IRC. (underlining and bold are mine)
- - M1501.1 Outdoor discharge. The air removed by every mechanical exhaust system shall be discharged to the outdoors. Air shall not be exhausted into an attic, soffit, ridge vent or crawl space.