First, I am presuming that the flex line as you referred to it is actually a flexible gas connector, in which case they are not allowed to be re-used (at least not by the main manufacturer of the flexible gas connectors - Note: place cursor over link, right click, then select 'Open in New Window' or similar option:
http://www.dormont.com/dmc/res/GasConnectors.aspx ). Once disconnected from the appliance the flexible connector needs to be removed and replaced (spec sheet
http://www.dormont.com/dmc/uploadedFile ... ectors.pdf , bottom of page 4), and if not replaced right away, then simply removed to allow for capping the gas line.
New Jersey has adopted the ICC codes, which includes the IRC. New Jersey has adopted amendments to the ICC codes, however, this section in the IRC has not been amended in the New Jersey IRC.
From the 2006 IRC and IRC New Jersey. (underlining and bold are mine)
- G2415.12 (404.12)
Outlet closures. Gas outlets
that do not connect to appliances shall be capped gas tight.
- - Exception: Listed and labeled flush-mounted-type quick-disconnect devices and listed and labeled gas convenience outlets shall be installed in accordance with the manufacturer’s installation instructions.
I am also contacting another very qualified person to see if he has additional comments for this.
Codeman