by Jerry Peck - Codeman on Thu Nov 22, 2012 10:05 pm
From the 2006 IRC:
- M1804.2 Termination. Vent termination shall comply with Sections M1804.2.1 through M1804.2.6.
- - M1804.2.1 Through the roof. Vents passing through a roof shall extend through flashing and terminate in accordance with the manufacturer’s installation requirements.
- - M1804.2.2 Decorative shrouds. Decorative shrouds shall not be installed at the termination of vents except where the shrouds are listed and labeled for use with the specific venting system and are installed in accordance with the manufacturer’s installation instructions.
- - M1804.2.3 Natural draft appliances. Vents for natural draft appliances shall terminate at least 5 feet (1524 mm) above the highest connected appliance outlet, and natural draft gas vents serving wall furnaces shall terminate at an elevation at least 12 feet (3658 mm) above the bottom of the furnace.
- - M1804.2.4 Type L vent. Type L venting systems shall conform to UL 641 and shall terminate with a listed and labeled cap in accordance with the vent manufacturer’s installation instructions not less than 2 feet (610 mm) above the roof and not less than 2 feet (610 mm) above any portion of the building within 10 feet (3048 mm).
- - M1804.2.5 Direct vent terminations. Vent terminals for direct-vent appliances shall be installed in accordance with the manufacturer’s installation instructions.
- - M1804.2.6 Mechanical draft systems. Mechanical draft systems shall be installed in accordance with their listing, the manufacturer’s installation instructions and, except for direct vent appliances, the following requirements:
- - - 1. The vent terminal shall be located not less than 3 feet (914 mm) above a forced air inlet located within 10 feet (3048 mm).
- - - 2. The vent terminal shall be located not less than 4 feet (1219 mm) below, 4 feet (1219 mm) horizontally from, or 1 foot (305 mm) above any door, window or gravity air inlet into a dwelling.
- - - 3. The vent termination point shall not be located closer than 3 feet (914 mm) to an interior corner formed by two walls perpendicular to each other.
- - - 4. The bottom of the vent terminal shall be located at least 12 inches (305 mm)above finished ground level.
- - - 5. The vent termination shall not be mounted directly above or within 3 feet (914 mm) horizontally of an oil tank vent or gas meter.
- - - 6. Power exhauster terminations shall be located not less than 10 feet (3048 mm) from lot lines and adjacent buildings.
- - - 7. The discharge shall be directed away from the building.
From the above, there are not specific requirements addressing this part of your question:
- Whats the clearance of a natural draft B vent to operable window, door, deck?
There is a requirement for this part of your question:
- Vert wall?
- G2427.6.4 (503.6.4) Gas vent termination. A gas vent shall terminate in accordance with one of the following:
- - 1. Gas vents that are 12 inches (305 mm) or less in size and located not less than 8 feet (2438 mm) from a vertical wall or similar obstruction shall terminate above the roof in accordance with Figure G2427.6.4.
- - 2. Gas vents that are over 12 inches (305 mm) in size or are located less than 8 feet (2438 mm) from a vertical wall or similar obstruction shall terminate not less than 2 feet (610 mm) above the highest point where they pass through the roof and not less than 2 feet (610 mm) above any portion of a building within 10 feet (3048 mm) horizontally.
- - 3. As provided for direct-vent systems in Section G2427.2.1.
- - 4. As provided for appliances with integral vents in Section G2427.2.2.
- - 5. As provided for mechanical draft systems in Section G2427.3.3.
If the gas vent is *not* less than 8 feet from a vertical wall or similar obstruction, then the gas vent shall terminate in accordance with Figure G2427.6.4. That Figure also includes a table of minimum vent heights above sloped roofs as follows:
ROOF SLOPE --> H (minimum) ft
Flat to 6/12 slope --> 1.0 ft
Over 6/12 slope to 7/12 slope --> 1.25 ft high minimum
Over 7/12 slope to 8/12 slope --> 1.5 ft high minimum
Over 8/12 slope to 9/12 slope --> 2.0 ft high minimum
Over 9/12 slope to 10/12 slope --> 2.5 ft high minimum
Over 10/12 slope to 11/12 slope --> 3.25 ft high minimum
Over 11/12 slope to 12/12 slope --> 4.0 ft high minimum
Over 12/12 slope to 14/12 slope --> 5.0 ft high minimum
Over 14/12 slope to 16/12 slope --> 6.0 ft high minimum
Over 16/12 slope to 18/12 slope --> 7.0 ft high minimum
Over 18/12 slope to 20/12 slope --> 7.5 ft high minimum
Over 20/12 slope to 21/12 slope --> 8.0 ft high minimum
However ... if the vent *is* within 8 feet of a vertical wall or similar obstruction, then the vent ... shall terminate not less than 2 feet above the highest point where they pass through the roof and not less than 2 feet above any portion of a building within 10 feet horizontally.
Thus, if the vent is within 8 feet of the vertical wall with the window or door in it, then the vent shall terminate as stated just above - "not less than 2 feet above any portion of a building within 10 feet horizontally". That means the vent must be at least 8 feet from the window or door (that would be the closest the vent could be to the wall the window or door is in), and if the vent is less than that 8 feet from the wall, then the vent need to be 2 feet higher than any portion of the building within 10 horizontally of the vent.
Any easy way to remember all the above is: 8 feet minimum horizontally from the window or door, or 2 feet higher than the highest part of the wall/roof within 10 feet of the vent.
That was a roundabout way to get to your answer, but sometimes the code does that.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired