by Jerry Peck - Codeman on Tue Oct 17, 2017 4:10 pm
Unless there is a Connecticut code which addresses vapor retarders/barriers other than in the Energy Code or Existing Building Code, and the referenced IRC, then, no, there are no requirements for vapor barriers/retarders - however, when installed, vapor retarders are to be installed in accordance with the manufacturer's installation instructions, such as on faced fiberglass batt insulation.
That said, here are some code sections to start with as the work you are describing should start under the Existing Building Code, specficially in Connecticut, the:
- 2012 IEBC (International Existing Building Code)
- - Section 202 General Definitions
- - Addition. An extension or increase in floor area, number of stories, or height of a building or structure
Alteration. Any constsruction or renovation to an existing structure other than a repair or addition. Alterations are classifed as Level 1, Level 2, and Level 3.
- - Change of Occupancy. A change in the purpose or level of activity within a building that involves a change of application of the requirements of this code.
- - Section 504 Alteration - Level 2
- - - 504.1 Scope.
- - - - Level 2 alterations include the reconfiuration of space, the addition or elimination of any door or window, the reconfiguration or extension of any system, or the installation of any additional equipment.
- - - 506 Change of Occupancy
- - - - Change of occupancy provisions apply where the activity is classified as a change of occupancy as defined in Chapter 2.
- - - - 506.2
- - - - - Changes of occupancy shall comply with the provisions of Chapter 10.
- - - Section 1001 General
- - - - 1001.2.1 Repair and alteration with no change of occupancy classification.
- - - - - Any repair or alteration work undertaken in connection with a change of occupancy that does not involve a change of occupancy classification shall conform to the applicable requirements for the work as classified in Chapter 4 and to the requirements of Sections 1002 through 1011.
- Chapter 8 is Level 2 Alteration
- - Section 811 Energy Conservation
- - - 811.1 Minimum requriements.
- - - - Level 2 alterations to existing buildings or structures are permitted without requiring the entire building or structure to comply with the energy requirements of the International Energy Conservation Code or the International Residential Code. The alterations shall conform to the energy requriements of the International Energy Conservation Code or International Residential Code as they relate to new construction only.
From the 2012 IRC, referenced in 8.11.1
- N1102.1.10 (R402.2.10) Crawlspace walls.
- - (R402.2.10 is the IECC Section for the same thing)
These sections address vapor retarders in crawlspaces.
All the above said, though, follow what your local AHJ (Authority Having Jurisdiction) says - makes life easier.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired