Hi Jerry,
Stone Masonry Veneer
Stone Masonry Veneer cladding is install below grade noted.
no drainage plane.
This is a comment from the builder. Simulated Masonry Veneer
This project has a simulated stone veneer; which is considered to be Adhered Manufactured
Stone Masonry Veneer. There is not currently a standard relating to this product. A new
committee has been formed to formulate a standard. :
http://www.astmnewsroom.org/default.aspx?pageid=1066
(See attached EX3)
It has been considered from this Industry for the product to fall under ASTM C 926 &
C1063. Requirements for installation to follow manufacture recommendations’. Installations
of the simulated stone veneer from River Valley Stone Products; was installed from an
approved company on this project. Requirements for FBCR R703.7 does not apply being
product & attachment is not addressed in this section. When product is not addressed
directly in the code or a referenced standard it is left up to manufacture specifications per:
SECTION R703
EXTERIOR COVERING
R703.1 General. Exterior walls shall provide the building with
a weather-resistant exterior wall envelope. The exterior wall
envelope shall include flashing as described in Section R703.8.
The exterior wall envelope shall be designed and constructed in
such a manner as to prevent the accumulation of water within
the wall assembly by providing a water-resistive barrier behind
the exterior veneer as required by Section R703.2. All exterior
finishes shall be applied in accordance with the manufacturer’s
specifications or installation instructions.
We are meeting this above section by providing a water-resistive barrier behind the exterior
veneer, i.e. exterior paint system installed behind the veneer. Concerns of wicking through
ground contact are in consequential; the simulated stone is sealed from the manufacture.
The mortar has a silicone waterproofing agent added to the mix. Any water entering will be
picked up from the drainage plane that exists through the exterior coating systems. Astm C
926 does not limit application below ground when applied to a masonry base.