New postby Greg Hatfield on Sun Jun 10, 2018 7:18 pm

Hi-wall mini-split indoor units use tubing to gravity feed condensate outdoors with pitch per their IOMs. They do not have to overcome static and several mfgs I checked do not mention inline check valves or ptraps as required by 307.2.4.1, let alone require one. FBC copies ICC so what was ICC thinking when they inserted this section? Now that it is part of the code, an inspector is requiring one or the other despite arguments that mfgs do not want either installed on their hi-wall unit drains. Higher static duct models and cassettes come with a condensate pump so not required. What are your thoughts? Thanks, Greg Hatfield
Greg Hatfield
 
Posts: 2
Joined: Tue May 15, 2018 5:24 pm

Re: FBC Mechanical 307.2.4.1

New postby Jerry Peck - Codeman on Sun Jun 10, 2018 8:00 pm

Greg,

First, some questions:

- Is this in a one- or two-family dwelling or a townhouse, or in a "commercial" building (i.e., 'other than' the aforementioned dwellings)?
- - The difference is the code which is applicable.

- What is the manufacturer and model mini-split?
- - I.e., we need to determine exactly what the manufacturer says about the installation.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: FBC Mechanical 307.2.4.1

New postby Jerry Peck - Codeman on Wed Jun 13, 2018 8:23 am

Jerry Peck - Codeman wrote: - What is the manufacturer and model mini-split?
- - I.e., we need to determine exactly what the manufacturer says about the installation.


The reason I asked that is if the manufacturer states to the effect of "do not trap", then installing a trap makes the installation noncompliant per the listing, labeling, manufacturer's installation instructions MII), and the code (the code requires compliance with the other items listed) ... and the code.

If the MII does not address trapping, then trapping that condescending drain would be required ... which brings us to the next part of the question - what would a compliant trap configuration be? Minimum / maximum water seal, among other trap dimension requirements.

Would a "running trap" be allowed? It us a "trap", but does no good, and in this case, potentially no harm.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm


Return to Mechanical: Heating and cooling equipment, duct work, ventilation and exhaust fans



Who is online

Users browsing this forum: No registered users and 2 guests


cron