Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

THIS BOARD IS READ ONLY AS CODEMAN HAS RETIRED
NO NEW QUESTIONS WILL BE PROCESSED

|
AskCodeMan.com
|

Custom Search

b vent on furnace located in basement 2 feet from chimney

b vent on furnace located in basement 2 feet from chimney

New postby WARREN40 on Thu Feb 18, 2010 1:20 am

i installed a furnace in Detroit michigan and the inspector wants a b vent installed is this code it has a 6" flue
WARREN40
 
Posts: 1
Joined: Thu Feb 18, 2010 12:50 am

Re: b vent on furnace located in basement 2 feet from chimney

New postby Jerry Peck - Codeman on Thu Feb 18, 2010 10:18 pm

Hi Warren,

The type of vent has to do with the type of appliance, not the size of the vent.

Is it a natural draft gas furnace? If so, then a Type Gas Vent is what is required, the size based on many variables.

If it is a condensing gas furnace then it would need a different type of vent.

I've contacted someone for additional input, if you could provide the type of furnace for him it would help with the answer.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: b vent on furnace located in basement 2 feet from chimney

New postby Hearthman on Thu Feb 18, 2010 10:51 pm

Warren, you didn't provide much info. so I'm not sure what you're dealing with or asking. Are you saying the AHJ wants you to install a B-vent in lieu of a listed liner in the chimney or is he asking you to use B-vent as a vent connector to the masonry chimney?

You must also consult the mfrs listed instructions. Some furnaces require a B-vent connector even in a conditioned space venting into an interior chimney. The codes and mfr much be consulted for specifics in vent connector sizing.

Modern 80% fan asisted furnaces run on such low stack temps, there is very little heat lost to warm the stack and thus create draft. The use of B-vent prevents stack connector losses, which helps draft while reducing condensation of flue gases. If this furnace does not have a post-purge cycle, one can easily be added, which will purge much of the moisture out of the stack and reduce condensation.

Is there a gas water heater common vented with this furnace?

Hearthman
Keep the fire in the fireplace.
Hearthman
 
Posts: 14
Joined: Sun Mar 01, 2009 9:49 pm
Location: Philly


Return to Mechanical: Heating and cooling equipment, duct work, ventilation and exhaust fans



Who is online

Users browsing this forum: No registered users and 2 guests


cron