b vent on furnace located in basement 2 feet from chimney

b vent on furnace located in basement 2 feet from chimney

New postby WARREN40 on Thu Feb 18, 2010 1:20 am

i installed a furnace in Detroit michigan and the inspector wants a b vent installed is this code it has a 6" flue
WARREN40
 
Posts: 1
Joined: Thu Feb 18, 2010 12:50 am

Re: b vent on furnace located in basement 2 feet from chimney

New postby Jerry Peck - Codeman on Thu Feb 18, 2010 10:18 pm

Hi Warren,

The type of vent has to do with the type of appliance, not the size of the vent.

Is it a natural draft gas furnace? If so, then a Type Gas Vent is what is required, the size based on many variables.

If it is a condensing gas furnace then it would need a different type of vent.

I've contacted someone for additional input, if you could provide the type of furnace for him it would help with the answer.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: b vent on furnace located in basement 2 feet from chimney

New postby Hearthman on Thu Feb 18, 2010 10:51 pm

Warren, you didn't provide much info. so I'm not sure what you're dealing with or asking. Are you saying the AHJ wants you to install a B-vent in lieu of a listed liner in the chimney or is he asking you to use B-vent as a vent connector to the masonry chimney?

You must also consult the mfrs listed instructions. Some furnaces require a B-vent connector even in a conditioned space venting into an interior chimney. The codes and mfr much be consulted for specifics in vent connector sizing.

Modern 80% fan asisted furnaces run on such low stack temps, there is very little heat lost to warm the stack and thus create draft. The use of B-vent prevents stack connector losses, which helps draft while reducing condensation of flue gases. If this furnace does not have a post-purge cycle, one can easily be added, which will purge much of the moisture out of the stack and reduce condensation.

Is there a gas water heater common vented with this furnace?

Hearthman
Keep the fire in the fireplace.
Hearthman
 
Posts: 14
Joined: Sun Mar 01, 2009 9:49 pm
Location: Philly