Custom Search
Page 1 of 1

crawl space distance to equipment

New postPosted: Mon Mar 07, 2011 10:27 pm
by chris mc
Codeman,
Had a HVAC contractor tell me today that the HVAC equipment must be within 20' of the crawl space access door per code.

I could not find this, or didn't know where to look, we are under the 2006 IRC.

Thanks in advance.

Re: crawl space distance to equipment

New postPosted: Tue Mar 08, 2011 12:03 am
by Jerry Peck - Codeman
Hi Chris,

That HVAC person is correct, unless exception 2 applies.
- M1305.1.4 Appliances under floors. Underfloor spaces containing appliances requiring access shall have an unobstructed passageway large enough to remove the largest appliance, but not less than 30 inches (762 mm) high and 22 inches (559 mm) wide, nor more than 20 feet (6096 mm) long when measured along the centerline of the passageway from the opening to the appliance. A level service space at least 30 inches (762 mm) deep and 30 inches (762 mm) wide shall be present at the front or service side of the appliance. If the depth of the passageway or the service space exceeds 12 inches (305 mm) below the adjoining grade, the walls of the passageway shall be lined with concrete or masonry extending 4 inches (102 mm) above the adjoining grade in accordance with Chapter 4. The rough-framed access opening dimensions shall be a minimum of 22 inches by 30
inches (559 mm by 762 mm), where the dimensions are large enough to remove the largest appliance.
- - Exceptions:
- - - 1. The passageway is not required where the level service space is present when the access is open, and the appliance can be serviced and removed through the required opening.
- - - 2. Where the passageway is unobstructed and not less than 6 feet high (1929 mm) and 22 inches wide for its entire length, the passageway shall not be limited in length.