Return air question

Return air question

New postby Marc M on Sun Aug 25, 2013 1:35 am

Hey Jerry,
just need clarification. Does this below exception underlined, say that you "can" have a return air near a fireplace etc...?

2010 CMC 311.3 Prohibited Source. Outside or return air for a heating
or cooling air system shall not be taken from the following
locations:


Exception: Such openings when used for a heating or
cooling air system in a dwelling unit shall be permitted
to be reduced to not less than 50 percent of the required area, provided the balance of the required return air is taken from a room or hall having not less than three (3) doors leading to other rooms served by the furnace.
(5) A closet, bathroom, toilet room, or kitchen.
(6) From rooms or spaces containing a fuel-burning appliance
therein.Where such room or space serves as source
of return air.
Exceptions:
(1) This shall not apply to fireplaces, fireplace appliance,
residential cooking appliance, direct vent
appliance, enclosed furnaces, and domestic-type
clothes dryers installed within the room or space
.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: Return air question

New postby Jerry Peck - Codeman on Sun Aug 25, 2013 11:10 am

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Return air question

New postby Marc M on Sun Aug 25, 2013 11:23 am

Go it, that will work. Detailed as usual...thanks for the help Jerry.