Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

THIS BOARD IS READ ONLY AS CODEMAN HAS RETIRED
NO NEW QUESTIONS WILL BE PROCESSED

|
AskCodeMan.com
|

Custom Search

GARAGE HVAC DUCT PENETRATION

GARAGE HVAC DUCT PENETRATION

New postby RICHARD TAN on Fri Apr 03, 2009 12:00 pm

Hi Jerry,

Duct penetration through the garage ceiling, required min. 26 gauge steel IRC 309.1.1.. Is rigid duct board acceptable material to penetrating the fire assembly?
RICHARD TAN
 
Posts: 60
Joined: Wed Jan 14, 2009 9:43 am

Re: GARAGE HVAC DUCT PENETRATION

New postby Jerry Peck - Codeman on Fri Apr 03, 2009 2:02 pm

Hi Richard,

First, the Florida Building Code, Residential has a similar requirement as the IRC for using 26 gage metal for that duct, however, duct board rated Class 0 or Class 1 IS a suitable alternative - however, the duct board would need to be labeled with such rating, otherwise I would write it up because the use of duct board is 'only allowed if rated Class 0 or Class 1'.

Third, that is not a "fire assembly", it is simply "separation".

From the Florida Building Code, Residential, with 2006 Revisions. (underlining and bold are mine)
- SECTION R309
- - GARAGES AND CARPORTS
- - - R309.1 Opening protection.
- - - - Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than 13/8 inches (35 mm) in thickness, solid or honeycomb core steel doors not less than 13/8 inches (35 mm) thick, or 20-minute fire-rated doors.
- - - R309.1.1 Duct penetration.
- - - - Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum No. 26 gage (0.48 mm) sheet steel, 1-inch (25 mm) minimum rigid nonmetallic Class 0 or Class 1 duct board, or other approved material and shall have no openings into the garage.
- - - R309.2 Separation required.
- - - - The garage shall be separated from the residence and its attic area by not less than ½-inch (12.7 mm) gypsum board applied to the garage side. Garages beneath habitable rooms shall be separated from all habitable rooms above by not less than 5/8-inch (15.9 mm) Type X gypsum board or equivalent. Where the separation is a floor-ceiling assembly, the structure supporting the separation shall also be protected by not less than ½-inch (12.7 mm) gypsum board or equivalent.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm


Return to Mechanical: Heating and cooling equipment, duct work, ventilation and exhaust fans



Who is online

Users browsing this forum: No registered users and 2 guests