by Jerry Peck - Codeman on Mon Dec 03, 2018 11:06 pm
First things first ... how do you get to the FBC-Plumbing from the FBC-Existing Buildings? (You start at the FBC-Existing Buildings for existing buildings.)
That said, if you start at the FBC-Existing Buildings, you ... stumble into a mis-mash of left out code to specifically ... take you anywhere specific ...
From the FBC-Existing Buildings (underlining is mine)
- (definitions)
- - [A]REPAIR. The reconstruction or renewal of any part of an existing building for the purpose of its maintenance or to correct damage.
Replacing a water heater would be considered a "repair" by the definition, however, unlike replacing water closets, replacing a water heater is not specifically ... specifically ... listed.
However ...
From the FBC-Existing Buildings (underlining is mine)
- 502.1 Scope.
- - Repairs, as defined in Chapter 2, include the patching or restoration or replacement of damaged materials, elements, equipment or fixtures for the purpose of maintaining such components in good or sound condition with respect to existing loads or performance requirements.
Thus, from the above, we can get to 'replacement of a water heater' in the FBC-Existing Buildings, and that it is a "repair".
(continuing from FBC-EB)
- 601.1 Scope.
- - Repairs as described in Section 502 shall comply with the requirements of this chapter and with the provisions of Section 706. Repairs to historic buildings need only comply with Chapter 12.
(Section 706 is for "existing roofing".)
The following is key to most things in the FBC-Existing Buildings: (bold and underlining are mine)
- 601.2 Conformance.
- - The work shall not make the building less conforming than it was before the repair was undertaken.
I.e., if a drain pan was not present before, not installing a drain pan when the water heater is replaced is not make it "less conforming that it was before".
- Section 101.1 Title.
- - These regulations shall be known as the Florida Building Code, Existing Building, hereinafter referred to as “this code.” In addition to the provisions of this chapter, [u]the provisions of Chapter 1, Florida Building Code, Building, shall govern the administration and enforcement of this code[/u].
That gets us to Chapter 1 of the full Administrative sections of the code, and Chapter 1 is the same for both FBC-Building, and FBC-Residential ... which can lead to the FBC-Residential plumbing chapters for water heater replacement in one- and two-family dwellings and townhouses - which is:
- CHAPTER 28
- - WATER HEATERS
and
- SECTION P2804
- - RELIEF VALVES
and
- P2801.6.1 Pan size and drain.
- - The pan shall be not less than 1 1/2 inches (38 mm) deep and shall be of sufficient size and shape to receive dripping or condensate from the tank or water heater. The pan shall be drained by an indirect waste pipe of not less than 3/4 inch (19 mm) diameter. Piping for safety pan drains shall be of those materials indicated in Table P2906.5. Where a pan drain was not previously installed, a pan drain shall not be required for a replacement water heater installation.
(Keep this from above in mind "The work shall not make the building less conforming than it was before the repair was undertaken")
Also, think logically - if the water heater was in the center area of a house ... how could you install a drain for the pan (and a pan without a drain is useless)?
(back to Relief Valves and discharge lines)
- P2804.6.1 Requirements for discharge pipe.
- - The discharge piping serving a pressure-relief valve, temperature relief valve or combination valve shall:
- - - 1. Not be directly connected to the drainage system.
- - - 2. Discharge through an air gap located in the same room as the water heater.
- - - 3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
- - - 4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
- - - 5. Discharge to the floor, to the pan serving the water heater or storage tank, to a waste receptor or to the outdoors.
- - - 6. Discharge in a manner that does not cause personal injury or structural damage.
- - - 7. Discharge to a termination point that is readily observable by the building occupants.
- - - 8. Not be trapped.
- - - 9. Be installed to flow by gravity.
- - - 10. Terminate not more than 6 inches (152 mm) and not less than two times the discharge pipe diameter above the floor or waste receptor flood level rim.
- - - 11. Not have a threaded connection at the end of the piping.
- - - 12. Not have valves or tee fittings.
- - - 13. Be constructed of those materials indicated in Section P2906.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.
- - - 14. Be one nominal size larger than the size of the relief-valve outlet, where the relief-valve discharge piping is constructed of PEX or PE-RT tubing. The outlet end of such tubing shall be fastened in place.
Read #2 and #5 again - they are not contradictory:
- 2 requires an air gap in the same room or space as the water heater
- 5 says that the discharge from the air gap may go to ... (gives choices)
Did they install the senor on the floor under/next to the water heater when they installed the auto shut off valve?
Logic and common sense come into play here:
- 1a) the purpose of the sensor is to detect a leak
- 1b) the purpose of the auto shut off valve is to shut the water off if a leak is detected and not damage anything inside
- 2) the purpose of the pan and drain is to allow leaking water to drain outside and not damage anything inside
- doesn't 1a and 1b solve the problem as well as 2?
- 3) and ... Keep this from above in mind "The work shall not make the building less conforming than it was before the repair was undertaken"
- 4) doesn't 3) allow 2), and isn't that actually better than "Where a pan drain was not previously installed, a pan drain shall not be required for a replacement water heater installation."?
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired