Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|

Custom Search

"Readily Accessible" Main Water shut off location

"Readily Accessible" Main Water shut off location

New postby pbennett1 on Fri Aug 07, 2009 2:28 pm

Is there a readily acessisble main water shut off location requirement with regards to height?
The attached photo shows this location not to be readily accessible, high above the water heater.
You do not have the required permissions to view the files attached to this post.
pbennett1
 
Posts: 12
Joined: Tue May 12, 2009 7:30 pm

Re: "Readily Accessible" Main Water shut off location

New postby Jerry Peck - Codeman on Fri Aug 07, 2009 4:13 pm

Hi Peter,

From the 2006 IRC. (underlining and bold are mine)
- P2903.9 Valves. Valves shall be installed in accordance with Sections P2903.9.1 through P2903.9.3.
- - P2903.9.1 Service valve. Each dwelling unit shall be provided with an accessible main shutoff valve near the entrance of the water service. The valve shall be of a full-open type having nominal restriction to flow, with provision for drainage such as a bleed orifice or installation of a separate drain valve. Additionally, the water service shall be valved at the curb or property line in accordance with local requirements.

- ACCESSIBLE. Signifies access that requires the removal of an access panel or similar removable obstruction.

The valve does not need to be "readily accessible", only "accessible". However, "accessible" does not state that it includes the use of ladders, only removable panels or similar removable items.

Thus, if the valve is high enough to need a ladder or step stool to reach the valve, the valve is not "accessible".
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm


Return to Plumbing: Water heaters, fixtures, traps, hose bibbs, water pressure, supply & DWV piping



Who is online

Users browsing this forum: No registered users and 1 guest