Is flexible corrugated copper supply line ( see: Image ) an approved piping material under IRC P2905.4? If so, why can it not be used for residential water heater TPR drain line tubing?

Thanks,

Aaron
"What the plainspoken man lacks in subtlety he makes up in clarity." - A.D. Miller

www.texasinspector.com
User avatar
aaronm
 
Posts: 62
Joined: Fri Jan 09, 2009 8:02 am

Re: Flexible Corrugated Copper Supply Piping

New postby Jerry Peck - Codeman on Tue May 24, 2011 9:58 pm

Aaron,

aaronm wrote:Is flexible corrugated copper supply line an approved piping material under IRC P2905.4?


You mean P2905.5 in the 2009 IRC or P2904.5 in the 2006 IRC? The table is for water distribution pipe versus 2009 IRC P2905.4 which is for water service pipe?

Yes, that is just 'copper tubing' which has been physically shaped to be 'flexible' (I used single quotes as it is not "flexible" in the normal way one thinks of "flexible", it is more like "bendable" as it can be "bent" without deforming its shape unless the bend is too sharp).

If so, why can it not be used for residential water heater TPR drain line tubing?


Because that 'bendable' copper pipe is deformed such that it can readily be installed where it is not straight and thus will not "9. Be installed to flow by gravity." and because the deformations will restrict its ability to "9. Be installed to flow by gravity."due to the corrugations in the pipe.

Those 'bendable' piping connectors are suitable for size-wise as the size reduction restriction of "3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to an air gap." is referring to 'nominal trade size' and those 'bendable' piping connectors are sized in 'nominal trade sizes'.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm


Return to Plumbing: Water heaters, fixtures, traps, hose bibbs, water pressure, supply & DWV piping



Who is online

Users browsing this forum: No registered users and 3 guests


cron