Hey Jerry,
Can you check this install for me. Its a wet vent viewed from the attic. Left in image is WC and right is shower. Isnt the WC a minimum 3"? Sorry about the images, they were taken from far away.
Marc
You do not have the required permissions to view the files attached to this post.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: Wet vent

New postby Jerry Peck - Codeman on Sun Jan 06, 2013 12:14 am

Marc,

I saw your post when you posted it; however, I was out of town at the time and did not have my codes with me - does this help?

From the 2009 IRC (California may have amendments affecting this): (bold and underlining are mine)
- P3113.1 Size of vents. The minimum required diameter of individual vents, branch vents, circuit vents, vent stacks and stack vents shall be at least one-half the required diameter of the drain served. The required size of the drain shall be determined in accordance with Chapter 30. Vent pipes shall be not less than 11/4 inches (32 mm) in diameter. Vents exceeding 40 feet (12 192 mm) in developed length shall be increased by one nominal pipe size for the entire developed length of the vent pipe.

I believe you are thinking of the drain size for the water closet.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm


Return to Plumbing: Water heaters, fixtures, traps, hose bibbs, water pressure, supply & DWV piping



Who is online

Users browsing this forum: No registered users and 3 guests