Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|

Custom Search

Electrical water heater, no impact protection.

Electrical water heater, no impact protection.

New postby RICHARD TAN on Thu Mar 26, 2009 11:48 am

Electrical water heater, no impact protection.
RICHARD TAN
 
Posts: 60
Joined: Wed Jan 14, 2009 9:43 am

Re: Electrical water heater, no impact protection.

New postby Jerry Peck - Codeman on Thu Mar 26, 2009 12:36 pm

Hi Richard,

All water heaters, appliances, and equipment installed in a garage require protection from vehicle impact.

This could be by installing bollard, raising the water heater/appliance/etc. on a structural platform (typically concrete blocks filled with concrete, to a minimum height of 24 inches is used for this) or supported from above at a height of at least 6 feet.

From the 2004 Florida Building Code - Residential, with 2006 Revisions: (bold and underlining are mine)
- P2801.2 Installation.
- - Water heaters shall be installed in accordance with this chapter and Chapters 20 and 24.
- P2801.6 Water heaters installed in garages.
- - Water heaters shall be installed in accordance with the manufacturer’s installation instructions which shall be available on the job site at the time of inspection.
- M2005.1 General.
- - Water heaters shall be installed in accordance with the manufacturer’s installation instructions and the requirements of this code. Water heaters installed in an attic shall conform to the requirements of Section M1305.1.3. Gas-fired water heaters shall conform to the requirements in Chapter 24. Domestic electric water heaters shall conform to UL 174 or UL 1453. Commercial electric water heaters shall conform to UL 1453. Oiled-fired water heaters shall conform to UL 732.

In reading any water heater manufacturer's installation instructions, one of the cautions listed with regard to installation in a garage is protection from vehicle damage. Below is just one example from a manufacturer's installation instructions (note - place cursor over link, right click, select 'Open in New Window' http://www.statewaterheaters.com/lit/im ... 71-000.pdf ).
- From the State Instruction Manual, Residential Electric Water Heaters. (Note that many manuals look like duplicates of each other with only the manufacturer's name changing.)
- - From page 8
- - - Locating The New Water Heater
- - - - second paragraph at top of right hand column
- - - - - Also, the water heater must be located and/or protected so it is not subject to physical damage by a moving vehicle.

The Florida Building Code - Residential, refers to the installation instructions and the installation instruction state that the water heater "must be located and/or protected so it is not subject to physical damage by a moving vehicle."

Hope that information helps.

Codeman
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Electrical water heater, no impact protection.

New postby RICHARD TAN on Thu Apr 02, 2009 11:34 am

Hi Jerry,

Is there a specific code just for the appliance protection?
RICHARD TAN
 
Posts: 60
Joined: Wed Jan 14, 2009 9:43 am

Re: Electrical water heater, no impact protection.

New postby Jerry Peck - Codeman on Thu Apr 02, 2009 11:56 am

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm


Return to Plumbing: Water heaters, fixtures, traps, hose bibbs, water pressure, supply & DWV piping



Who is online

Users browsing this forum: No registered users and 1 guest


cron