by Jerry Peck - Codeman on Thu Sep 08, 2016 3:31 pm
Trap, trap arm, fixture to trap?
Not really about a height above the floor, but this may (or maybe not) address what you are thinking:
- FBC-Residential (underlining is mine)
- - P3201.6 Number of fixtures per trap.
- - - Each plumbing fixture shall be separately trapped by a water seal trap. The vertical distance from the fixture outlet to the trap weir shall not exceed 24 inches (610 mm) and the horizontal distance shall not exceed 30 inches (762 mm) measured from the center line of the fixture outlet to the centerline of the inlet of the trap. The height of a clothes washer standpipe above a trap shall conform to Section P2706.2. Fixtures shall not be double trapped.
- - - - Exceptions:
- - - - - 1. Fixtures that have integral traps.
- - - - - 2. A single trap shall be permitted to serve two or three like fixtures limited to kitchen sinks, laundry tubs and lavatories. Such fixtures shall be adjacent to each other and located in the same room with a continuous waste arrangement. The trap shall be installed at the center fixture where three fixtures are installed. Common trapped fixture outlets shall be not more than 30 inches (762 mm) apart.
- - - - - 3. Connection of a laundry tray waste line into a standpipe for the automatic clothes-washer drain shall be permitted in accordance with Section P2706.2.1.