by Jerry Peck - Codeman on Tue Nov 18, 2014 7:18 pm
The electrician is correct that voltage drop is unenforceable, however, high voltage drop readings are a result of inadequate planning and (oftentimes) cost savings and poor workmanship.
I always referred to 90.1(B)
- 90.1 Purpose
- - (B) Adequacy. The code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance results in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.
"but not necessarily efficient, convenient, or adequate for good service"
And electricians and electrical contractors think that meeting the minimum requirements of the NEC is a real big deal - the NEC itself says it that meeting the NEC might not be adequate, efficient or convenient.
On any house over a entry level production house ... the NEC should never come up as penny-pinching only goes on in entry level-production houses.
Now to the actual problems:
The most likely cause is that they likely used back stabbed devices on their 15 amp circuits and back stabbing if a major cause of voltage drop.
Another likely cause (after backstabbing devices) is they likely have all the panels in one location (the garage) and now have to run 200 feet of wire to the other end of the house ... if they do not up-size the wire size they WILL have voltage drop issues.
The speedometer being off is not an applicable analogy, maybe this is - your car uses more fuel the faster you go, and saves fuel by driving slower, unless the car's computer is set wrong and then it drinks fuel like it's Kool-Aid ... and that is what voltage drop is doing - you don't have to be using the circuit at its maximum capacity to waste energy with voltage drop.
Additionally, may appliances and computers (and many appliances have computers in them) give a maximum range for the voltage, and the lower range may not be met if there is voltage drop. Let's say the circuit has 120 volts on it, a 15% voltage drop is 18 volts, which means the voltage is really only 102 volts ...
Voltage drop enforceable? Only after you get your clients to understand what voltage drop does to them and their appliances, and then THEY "enforce it" with the builder, and after the builder has to correct it a couple of time, the BUILDER "enforces it" with their electrician. I went through this with some high end builders in Palm Beach County, a few of them realized that the cost of pulling in #12 wire for 15 amps circuits was not much compared to the flack they got from their clients for having pulled in #14 and now had voltage drop.
Another solution is to go back to installing remote panels, one in the downstairs hall, another in the upstairs hall, that means the circuit length was dramatically reduced and voltage drop due to the length of the circuits was dramatically reduced.
The language I used to address voltage drop was 90.1(B), especially this part "but not necessarily efficient, convenient, or adequate for good service".
The NEC is about "safety", and "not necessarily efficient, convenient, or adequate for good service".
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired