by Jerry Peck - Codeman on Tue Jul 27, 2021 9:18 pm
Well ... the horizontal orientation does create quite a few issues ... (sorry, couldn't help it).
There is nothing wrong with the meter being on top of the panel per se, but there could be if it was done incorrectly.
I see a riser going vertically up (viewing the photo rotated counterclockwise 90 degrees) to what I suspect would be an overhead service. (f that is done correctly, no issues there.
Then I see it going down to the service equipment panel below through a nipple of some length, if done correctly, no issues there either.
Then I see various raceways coming out the bottom of the service equipment panel which look like they are going into the ground below, if done correctly, no issues there ... however, a common error is using Sch 40 PVC going the ground. Sch 40 is not suitable for protection from physical damage, Sch 80 is required from 18" below ground to 8' above ground or to the first enclosure (i.e., from 18" below ground to that service equipment enclosure).
The big and obvious code violation is that door which closes over the electrical equipment ... that's a big no-no.
And don't forget those bushes ... working space is to be open, no obstructions, and level. Working space size is minimum with of 30" or the width of the equipment if wider than 30" by 36" deep in front of the equipment, with access to the space (a minimum 24" wide access is acceptable, as I recall).
I had a few where the working space was on a sloping lot away from the building and the equipment, a few which were sloped down 2 feet in that 3 foot depth, and the contractors (builder and electrical) tried to blame each other, I told them to work it out because if the electrical does not pass, the building cannot be occupied, does not matter to me who corrects it, but the longer you two argue about, the longer it will take pass inspection, and no occupancy until it does - amazing how quickly they agreed to work together to correct it).
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired