Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|

Custom Search

Condo firewall seperation

Condo firewall seperation

New postby Marc M on Mon Apr 12, 2010 4:46 pm

Jerry, do you know what the firewall seperation is between two condos side by side. I thought is was 2 hour.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am

Re: Condo firewall separation

New postby Jerry Peck - Codeman on Mon Apr 12, 2010 5:32 pm

Hi Marc,

What you are referring to are "Fire Partitions" instead of "Fire Walls", with Fire Partitions being under Section 708. Fire partitions have a minimum required fire-resistance rating of not less than 1 hour, with exceptions allowed to 1/2 hour with automatic sprinkler systems meeting certain requirements.

From the 2006 IBC: (underlining and bold are mine)
- SECTION 708
- - FIRE PARTITIONS
- - - 708.1 General. The following wall assemblies shall comply with this section:
- - - - 1. Walls separating dwelling units in the same building.
- - - - 2. Walls separating sleeping units in occupancies in Group R-1 hotel, R-2 and I-1 occupancies.
- - - - 3. Walls separating tenant spaces in covered mall buildings as required by Section 402.7.2.
- - - - 4. Corridor walls as required by Section 1017.1.
- - - - 5. Elevator lobby separation as required by Section 707.14.1.
- - - - 6. Residential aircraft hangars.
- - - 708.2 Materials. The walls shall be of materials permitted by the building type of construction.
- - - 708.3 Fire-resistance rating. Fire partitions shall have a fire-resistance rating of not less than 1 hour.
- - - - Exceptions:
- - - - - 1. Corridor walls as permitted by Table 1017.1. (Jerry's note: This section allows the walls between the corridor and the dwelling unit to be 0.5 hours R occupancies with a sprinkler system meeting certain requirements.)
- - - - - 2. Dwelling and sleeping unit separations in buildings of Type IIB, IIIB and VB construction shall have fire-resistance ratings of not less than 1/2 hour in buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1.

Keep in mind, though, that a 1/2 hour fire-resistance rated wall is constructed the same as a 1 hour fire-resistance rated wall.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm

Re: Condo firewall seperation

New postby Marc M on Mon Apr 12, 2010 6:33 pm

Fantastic, thank you.
Marc M
 
Posts: 173
Joined: Sat May 09, 2009 10:24 am


Return to Drywall / gypsum board: non-fire resistance rated; Type X fire-resistance rated; plaster board (blue board); rock lath (for plastering); exterior gypsum sheathing



Who is online

Users browsing this forum: No registered users and 3 guests


cron