New postby garrett on Sat Sep 03, 2011 1:12 pm

How far from a vent stack can the kitchen drain be located?
Thank you,
Garrett
garrett
 
Posts: 6
Joined: Thu Apr 28, 2011 1:34 pm

Re: Plumbing ?

New postby Jerry Peck - Codeman on Sat Sep 03, 2011 2:37 pm

The answer depends on the size of the pipe from the trap to the vent, the pipe is required to slope 1/4 inch per foot for 2 inches and smaller, which means smaller pipe must be shorter in length to allow the pipe to remain open and vented.
- 1-1/2 inch pipe is allowed to have a maximum distance of 6 feet from the weir of the trap to the vent.
- 2 inch pipe is allowed to have a maximum distance of 8 feet from the weir of the trap to the vent.

3 inch and 4 inch pipe are allowed greater distances, not only because they are larger in size, but also because their slope is only required to be 1/8 inch per foot, but you would not have pipe that size for the kitchen drain.

Keep in mind that if you slope a pipe greater than the 1/4 inch per foot, or greater than the 1/8 inch per foot, the allowable distance is going to become considerably shorter the more the pipe is sloped.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1199
Joined: Fri Dec 12, 2008 12:06 pm


Return to Plumbing: Water heaters, fixtures, traps, hose bibbs, water pressure, supply & DWV piping



Who is online

Users browsing this forum: No registered users and 5 guests