by Jerry Peck - Codeman on Wed Oct 19, 2011 7:59 pm
You are correct in that sound transmission, air-borne sound and structure-borne sound, did not enter the code until the 2004 Florida Building Code, as such, the only requirement for sound transmission would be in the construction documents by the architects/engineers - that would best be found in the specifications book(s) for the project.
The ironic aspect of air-borne sound is that the sound transmission class (STC) construction is proprietary and was designed by each manufacturer of gypsum board, therefore, to meet the minimum stated STC rating of 50, the walls would need to be constructed in accordance with the sound transmission class designs from one specific manufacturer, and the gypsum board *from that specific manufacturer would need to be used throughout one entire story* unless there as a break against a shear wall, elevator shaft, or stair tower which went from one exterior wall to the interior corridor.
This is because the gypsum board on the other side of the wall also had to be the same manufacturer as was on the first side of the wall, otherwise the STC rating was invalid and would need to be field tested.
It was much simpler to use one manufacturer's gypsum board on each floor, changing brands from floor to floor is the supply was not adequate from one manufacturer for the entire high-rise.
The 2001 Florida Building Code allowed for the use of sound deadening board on floors, but did not require its use.
Now, to answer what I suspect your question is (correct me if I am wrong): If an existing condo building is being renovated, does it have to comply with the current codes which address sound transmission, or can it remain as it was originally constructed? That depends on the extent of the work being done, but it would take a lot of work to require bringing the entire building up to current code. All new work would first need to meet the Florida Building Code, Existing Building, and that would guide you to what extent the Florida Building Code, Building, Mechanical, Plumbing, National Electrical Code, etc., would apply.
The short answer, and which would probably be correct the vast majority of the time, would be that the existing building would not be required to meet the sound transmission requirements ... unless the condo board said it did (after all, the structure is one common structure and is owned by the condo association).
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired