Pool system bonding

New postby bigdog on Mon Dec 22, 2014 9:05 pm

Hey Jerry
What is the required fix for pools where no bond wire to the pool shell etc. can be found? Shouldn't it have to be fixed to current standards as in chipping into the concrete pool beam and attaching another (or maybe the first) bond wire to it and running back to the pump (at a minimum?).

I can't tell you how many times I get called back to re-inspect and find a driven ground rod connected to the pool pump motor.

Also I remember reading a history of the bonding requirements and seem to remember that a bond wire wasn't even a requirement until the 90"s.

What say yee.

David McCabe
bigdog
 
Posts: 85
Joined: Thu Apr 12, 2012 10:54 pm

Re: Pool system bonding

New postby Jerry Peck - Codeman on Mon Dec 22, 2014 10:09 pm

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Pool system bonding

New postby Jerry Peck - Codeman on Mon Dec 22, 2014 10:21 pm

I started with my 1968 NEC (it may be in the 1965, but it was not as I recall, and I didn't recheck it right now):

(too much to type, but I'll list the highlights of what it includes)
- 608-7 Grounding.
- - (a) The following parts shall be bonded together by a copper conductor not smaller than No. 8 AWG:
- - - (the highlights)
- - - pool reinforcing steel (steel tie wires are permitted to tie the steel together)
- - - metal ladder parts
- - - diving boards and their supports and the like
- - - metal parts of electrical equipment associated with the water circulating system
- - - all fixed metal parts within 5 feet of the water and not separated by a permanent barrier
- - (b) Where the swimming pool light ...
- - - No. 12 AWG copper can serve as the bonding conductor
- - (c) metallic raceways shall not be depended upon except between the forming shell and junction box
- - - No. 12 AWG copper can serve as the bonding conductor
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired