by Jerry Peck - Codeman on Mon Jun 08, 2015 2:49 pm
If the exit enclosure's exterior walls meets this: (bold and underlining are mine)
- 705.5 Fire-resistance ratings. Exterior walls shall be fire-resistance rated in accordance with Tables 601 and 602 and this section. The required fire-resistance rating of exterior walls with a fire separation distance of greater than 10 feet (3048 mm) shall be rated for exposure to fire from the inside. The required fire-resistance rating of exterior walls with a fire separation distance of less than or equal to 10 feet (3048 mm) shall be rated for exposure to fire from both sides.
Then the exit enclosure's exterior walls should be good as they would meet the code's requirements for fire-resistance rating based on the Type of Construction and Occupancy as required and shown in Table 601 and Table 602.