Building Code and Building Construction - Questions and Answers
Or when you want to know how construction is supposed to be done.

|
AskCodeMan.com
|

Custom Search

Smurf wiring in crawl space

Smurf wiring in crawl space

New postby Timham on Thu Feb 09, 2017 6:15 pm

Hi Jerry,

Can ENT be installed in a crawl space?
Timham
 
Posts: 9
Joined: Thu Dec 15, 2016 10:10 pm

Re: Smurf wiring in crawl space

New postby Jerry Peck - Codeman on Thu Feb 09, 2017 6:46 pm

Yes.

Now for the fun part though - the conductors in the ENT are required to be suitable for wet or damp locations (a crawlspace is a damp location, and the interior of raceways in damp locations or wet locations are rated the same as the location the raceway is in) thus the conductors would likely need to be THHN/THWN (dual listed) - will be on each conductor - they may be THW or some other type suitable for wet locations (THW has a lower temperature rating that THWN has), basically look for a "W" in the type of insulation on the conductors.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm


Return to Electrical: Service Equipment, electrical panels, wiring, lighting, switches, receptacles, etc.



Who is online

Users browsing this forum: No registered users and 1 guest


cron