Fire wall-separation between garage and living space

Fire wall-separation between garage and living space

New postby insight on Mon Oct 19, 2009 3:17 pm

What is the effective date for fire retardant materials between a built-in garage and a finished basement, including the passage door, for the main level living space for single family residence? A Code reference number would be appreciated.
insight
 
Posts: 8
Joined: Sun Oct 18, 2009 11:29 pm

Re: Fire wall-separation between garage and living space

New postby Jerry Peck - Codeman on Mon Oct 19, 2009 7:22 pm

First, just letting you know these are not "Private Questions" (which are set up to be password protected and not accessible to others - and only so for very specific reasons).

I will move this to the appropriate forum for the answer, okay?
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Fire wall-separation between garage and living space

New postby Jerry Peck - Codeman on Mon Oct 19, 2009 9:59 pm

Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Fire wall-separation between garage and living space

New postby insight on Tue Oct 20, 2009 12:27 am

The area in question is North Carolina.
insight
 
Posts: 8
Joined: Sun Oct 18, 2009 11:29 pm

Re: Fire wall-separation between garage and living space

New postby Jerry Peck - Codeman on Tue Oct 20, 2009 10:17 am

North Carolina is under the ICC codes, for dwelling units (1 and - 2 family dwellings and townhouses) that would be the IRC.

Previously, as with most of the southeastern US, North Carolina was using the Standard Codes from SBCCI (the predecessor to the ICC).

The 1988 Standard Building Code required a 1-3/4" solid wood between the house and the garage, and it was to be self-closing and self-latching (under certain conditions), however, actually separation was not required between the garage and the dwelling.

I will go through some of my other codes and try to find when separation was required. I do know that many AHJ which used the Standard Building Code required separation using at least 1/2" gypsum board on the garage side. Back then discussions about what to call that wall were on-going as that wall was not a "fire-rated" wall, which gets back the the 'non-fire rated assembly' I referred to in my previous post.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Fire wall-separation between garage and living space

New postby insight on Thu Oct 22, 2009 3:42 pm

Any other updates?
insight
 
Posts: 8
Joined: Sun Oct 18, 2009 11:29 pm

Re: Fire wall-separation between garage and living space

New postby Jerry Peck - Codeman on Thu Oct 22, 2009 4:08 pm

The 1994 Standard Building Code states:
- B411.2.6 Automobile parking garages shall be separated from other occupancies in accordance with B704.
- - EXCEPTION: Separation is not required between a Group R3 building and an attached garage.

- R3: Residential occupancies including the following:
- - Child care facilities which accommodate five or less children of any age for any time period.
- - One and two family dwellings where the occupants are primarily permanent in nature and not classified as R1, R2, or I.

The 1997 puts a new twist in that section by changing the wording, and thus confusing the situation:
- B504 BUILDINGS LOCATED ON THE SAME LOT
- - Where the exterior walls of two or more buildings located on the same lot face one another, and one of the walls is not constructed as required for a fire wall, a property line shall be assumed between them. The fire resistance requirements for such facing walls and for the protection of openings therein shall be the same as required by this code for walls and openings facing an assumed property line, as provided in Table B600.
- - - EXCEPTION: Fire resistance separation shall not be required between a dwelling and its detached private garage.

That has since become simply "separation" IS required in the newer codes, and the reference to "fire resistance" has been dropped as "separation" and "fire resistance" rated assemblies are two different things.

The code following the 1997 Standard Building Code was the 2000 IRC, which the change to "separation" became official and is required to be the same as is today.
Jerry Peck - CodeMan
AskCodeMan.com
Construction Litigation Consultant - Retired
Construction and Code Consultant - Semi Retired
User avatar
Jerry Peck - Codeman
Site Admin
 
Posts: 1201
Joined: Fri Dec 12, 2008 12:06 pm

Re: Fire wall-separation between garage and living space

New postby insight on Thu Oct 22, 2009 4:52 pm

Thanks for the info
insight
 
Posts: 8
Joined: Sun Oct 18, 2009 11:29 pm